06-01-2011, 10:31 AM #1
undersized condenser
hi all went to a new Condenser installation by our company today aw43lmyb3 1.4kw low temp and found it controlling a muller mnd029 2.9kw . 15mtr horizontal pipe run . found evap iced in morning ,cleared and adjusted defrost settings , later afternoon found evap iced again and maintain max -7c . then found condenser undersized and old tx valve still on 502 require replacement . suction not to bad on 404a
suc/ -20
dis/ 45 c @ 30c amb.
As this is an incorrect installation is the evap coil forming ice within 10mins a main sign of an undersized condenser not feeding evap , or should i replace the tx valve and possibly get the system to perform ?
There is other issues with using another condenser
Single phase unit not available anymore
no space to install unit as its on a rack and new units are increased dimensions .
- One of our techs has already quoted this job and now i need to clean mess up quickly ! thanks for any input
-
06-01-2011, 11:49 PM #2
Re: undersized condenser
Have you changed old tx valve?
-
07-01-2011, 12:35 AM #3
Re: undersized condenser
Acura, i would have expected compressor to go out on high pressure with poor cooling performance. Suspect evap icing up due to high load/humidity in room. If suction around 270kpa, system cannot be correctly charged, 502 valve or not. Really only one solution, more condenser needed. Suppose setting up a hose as temporary fix.. mike.
To the optimist, the glass is half full. To the pessimist, the glass is half empty.
-
07-01-2011, 06:27 AM #4
Re: undersized condenser
fit the correct tev and check gas charge and check superheat and sub cooling to see how system is performing
-
09-01-2011, 01:12 AM #5
Re: undersized condenser
thanks for reply.
returned and replaced tx valve checked unit details further heatcraft only rate the condenser to -20c 1400watts evap is 3kw ! im only getting room temp -7c it cant go any lower . Have organised with company to supply 3 phase and install larger condenser . gave option to replace evap as well . Advised them we made mistake and will rectify they are happy we will resolve it .
-
09-01-2011, 01:15 AM #6
Re: undersized condenser
Hi i was suprised it didnt have higher head press, pressure looked pretty good , we are replacing with 3phase cond , as i put in post unit only rated to -20c 1400w evap 3000watt thats where the mistake was made the young bloke learnt a lesson hard
Similar Threads
-
Install condenser in opposite position its built for?
By Henry. in forum FundamentalsReplies: 24Last Post: 19-08-2010, 10:50 PM -
Parallel condensers Shell and tube paralle with Evaporative Condenser
By Herschmidt in forum NH3Replies: 2Last Post: 08-06-2010, 11:12 PM -
How to measure COP (evaporative condenser)
By Juho in forum Technical DiscussionsReplies: 5Last Post: 04-06-2010, 07:08 PM -
Evaporative Condenser system COP
By Juho in forum CommercialReplies: 0Last Post: 03-06-2010, 09:23 AM -
Air Cooled Condenser Leakage Problem with R-404A
By RADHAKRISHNARAO in forum Technical DiscussionsReplies: 19Last Post: 30-07-2008, 12:21 PM