    undersized condenser

    hi all went to a new Condenser installation by our company today aw43lmyb3 1.4kw low temp and found it controlling a muller mnd029 2.9kw . 15mtr horizontal pipe run . found evap iced in morning ,cleared and adjusted defrost settings , later afternoon found evap iced again and maintain max -7c . then found condenser undersized and old tx valve still on 502 require replacement . suction not to bad on 404a

    suc/ -20
    dis/ 45 c @ 30c amb.


    As this is an incorrect installation is the evap coil forming ice within 10mins a main sign of an undersized condenser not feeding evap , or should i replace the tx valve and possibly get the system to perform ?
    There is other issues with using another condenser
    Single phase unit not available anymore
    no space to install unit as its on a rack and new units are increased dimensions .
    - One of our techs has already quoted this job and now i need to clean mess up quickly ! thanks for any input

  2. #2
    Join Date
    Jan 2011
    Location
    Australia
    Posts
    16
    Rep Power
    0

    Re: undersized condenser

    Have you changed old tx valve?

  3. #3
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,762
    Rep Power
    32

    Re: undersized condenser

    Acura, i would have expected compressor to go out on high pressure with poor cooling performance. Suspect evap icing up due to high load/humidity in room. If suction around 270kpa, system cannot be correctly charged, 502 valve or not. Really only one solution, more condenser needed. Suppose setting up a hose as temporary fix.. mike.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  4. #4
    Join Date
    Mar 2009
    Location
    australia
    Age
    42
    Posts
    12
    Rep Power
    0

    Re: undersized condenser

    Hi i was suprised it didnt have higher head press, pressure looked pretty good , we are replacing with 3phase cond , as i put in post unit only rated to -20c 1400w evap 3000watt thats where the mistake was made the young bloke learnt a lesson hard

  5. #5
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: undersized condenser

    fit the correct tev and check gas charge and check superheat and sub cooling to see how system is performing

  6. #6
    Join Date
    Mar 2009
    Location
    australia
    Age
    42
    Posts
    12
    Rep Power
    0

    Re: undersized condenser

    thanks for reply.

    returned and replaced tx valve checked unit details further heatcraft only rate the condenser to -20c 1400watts evap is 3kw ! im only getting room temp -7c it cant go any lower . Have organised with company to supply 3 phase and install larger condenser . gave option to replace evap as well . Advised them we made mistake and will rectify they are happy we will resolve it .

Similar Threads

  1. Replies: 24
    Last Post: 19-08-2010, 10:50 PM
  2. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  3. How to measure COP (evaporative condenser)
    By Juho in forum Technical Discussions
    Replies: 5
    Last Post: 04-06-2010, 07:08 PM
  4. Evaporative Condenser system COP
    By Juho in forum Commercial
    Replies: 0
    Last Post: 03-06-2010, 09:23 AM
  5. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •