    vector 1800 stop/start



    hi guys

    i was looking at a vector 1800 today not switching off on stop/start mode. battery voltage, water temp, amp draw ect all check out ok and ran it for longer than the minimum time periods. it would just cycle between heat and cool as it would on continuous mode. just wondering if there is anything else it could be before i knock it for a processor

    cheers paul



  2. #2
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: vector 1800 stop/start

    what temperature was it set for,some have cycling at temps close to freezing point set it on -15c and see what it does,

  3. #3
    Join Date
    Jul 2011
    Location
    England
    Age
    35
    Posts
    37
    Rep Power
    0

    Re: vector 1800 stop/start

    tried it at -20, +20 and everything inbetween. only thing i can think of is trying a new battery

  4. #4
    Join Date
    Dec 2007
    Location
    Melbourne
    Posts
    349
    Rep Power
    18

    Re: vector 1800 stop/start

    I'd be trying the cheap battery option first too.
    Are there any auxillaries taking power from the fridge? like a second battery for a tailgate loader?

  5. #5
    Join Date
    Mar 2012
    Location
    UK
    Posts
    23
    Rep Power
    0

    Re: vector 1800 stop/start

    Check your amp draw. If its above 7amps the unit won't shut down. Fit a yellow top deep cycle battery- standard batteries don't last mate.

    I've also had the grey plug on the battery charger cause this fault. I'd recommend cutting the plug out and soldering the wiring.

    I had this- the amps look fine but then it starts to fluctuate. If the battery is ok, then I'd definitely cut the plug out and solder the wiring. Even if its just to eliminate it.

    Check battery volts, battery amps before and after.

    Good luck.
    Last edited by Top_cat; 28-03-2013 at 10:30 AM.

  6. #6
    Join Date
    Jan 2013
    Location
    usa
    Posts
    29
    Rep Power
    0

    Re: vector 1800 stop/start

    Yes the micro is not seeing the correct battery volts, water temp and set point. Usally carrier does not have issues with air sensors but...... Check your air sensors.

  7. #7
    Join Date
    Jul 2011
    Location
    England
    Age
    35
    Posts
    37
    Rep Power
    0

    Re: vector 1800 stop/start

    ill try a new battery next week as its just got a black TK one on and hopefully that will sort it

  8. #8
    Join Date
    Feb 2009
    Location
    telford
    Posts
    2,097
    Rep Power
    33

    Re: vector 1800 stop/start

    gel batteries should be fitted to these around 700 cca if memory serves me well,lead acid tend to get destroyed with vibration,over here ctc did a recall on a lot of units.

  9. #9
    Join Date
    Jul 2011
    Location
    England
    Age
    35
    Posts
    37
    Rep Power
    0

    Re: vector 1800 stop/start

    cadwaladr,

    problem is my company won't buy the gel ones as the trailer is on contract maintenance so they get the TK batteries dirt cheap and as you said they don't last

  10. #10
    Join Date
    Mar 2012
    Location
    UK
    Posts
    23
    Rep Power
    0

    Re: vector 1800 stop/start

    A new standard battery will last 6 months if your lucky chap. The cell nearest the positive always drys out first. As cadwaladr said Carrier spent a fortune sorting this issue.

    Has to be a yellow top jelly style battery dude
    Last edited by Top_cat; 03-04-2013 at 06:48 PM.

  11. #11
    Join Date
    Jul 2011
    Location
    England
    Age
    35
    Posts
    37
    Rep Power
    0

    Re: vector 1800 stop/start

    top_cat,

    tried new battery and removed the plug on the battery charger, no difference to amp draw, still 8.2amps but i didn't know they were set to shut down at 7 amps so that explains why it won't. but boss told me to just adjust the cut off point to 10amps in the settings, the unit shuts off straight away now but will this cause any problems being set to 10amps?

  12. #12
    Join Date
    Aug 2008
    Location
    Lincolnshire
    Posts
    13
    Rep Power
    0

    Re: vector 1800 stop/start

    You will just kill the battery even quicker and (probably) suffer from b/downs for flat battery. you need to find the route cause of the high amp draw not just mask it by altering settings.

  13. #13
    Join Date
    Sep 2006
    Location
    england
    Posts
    285
    Rep Power
    18

    Re: vector 1800 stop/start

    setpoint you are quite right also if he puts a tk battery on a unit not desgned for that battery carrier20amp charger tk could be5oamp charger