Thread: Daikin- E7 error code
-
05-01-2011, 05:52 PM #1
Daikin- E7 error code
Hi.
The Daikin air conditioner that we own stopped working all of a sudden. Following a search through the internet, I was able to find out using the remote control that the error code was E7. The E7 error code corresponds to a malfunction of the outdoor unit fan motor. How can I fix this?
Any help would be much appreciated.
-
05-01-2011, 06:54 PM #2
Re: Daikin- E7 error code
Malfunction of Outdoor Unit Fan Motor (E7)
Remote Controller
DisplayE7Method of
Malfunction
DetectionAbnormality of fan motor system is detected according to the fan speed detected by hall IC when the
fan motor runs.Malfunction
Decision
ConditionsWhen the fan runs with speed less than a specified one for 15 seconds or more when the fan motor
running conditions are met
When connector detecting fan speed is disconnected
When malfunction is generated 4 times, the system shuts down.
Supposed CausesMalfunction of fan motor
The harness connector between fan motor and PC board is left in disconnected, or faulty connector
Fan does not run due to foreign matters tangled
Clearing condition: Operate for 5 minutes (normal)
Troubleshooting
CautionBe sure to turn off power switch before connect or disconnect connector, or parts damage may be
occurred.
Replace the outdoor unit fan motor.
Connect the connector.
Remove the foreign matter.
YES
NO
Are fan motor
connectors
disconnected?
Replace the outdoor unit fan motor.
NO
YES
Is the pulse input?Check No. 11Check for pulse input(S2584
for number of rotations
on the outdoor unit
PC board.
Replace the outdoor unit PC board.
YES
NO
NO
YES
Is there
any foreign matter
around the fan?
Can the fan be
easily rotated by hand?
Similar Threads
-
Daikin not working... many problems
By stankovicv in forum Air ConditioningReplies: 26Last Post: 11-12-2010, 09:01 AM -
Daikin assistance or LACK of it!!
By brianocallaghan in forum Air ConditioningReplies: 7Last Post: 15-07-2010, 11:23 AM -
Mitsi City Multi VS Daikin VRV
By sumsor in forum FundamentalsReplies: 5Last Post: 14-07-2010, 05:54 PM -
Daikin AC parts from UK
By skel00 in forum Air ConditioningReplies: 5Last Post: 05-04-2009, 01:24 PM -
Fixing Daikin A3 Error
By Stuffy in forum Air ConditioningReplies: 3Last Post: 27-03-2009, 06:02 AM