    Displacement



    Hi Guys

    Can you help me in this :

    If a compressor with a displacement of 10 meter cube hour is displacing gas with a pressure of 10 bar, it is displacing 100 meter cube hour ??
    (10 meter cube x 10 bar)

    Marco



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: Displacement

    NO, the specification of 10m3/hr at 10 bar means just that.

    If the disharge pressure is at 10 bar then the compressor can only pump 10m3/h.

    If, however, the pressure drops then the compressor may be able to pump more as the resistance has fallen.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Displacement

    Exactly. The displacement is the volume swept by the pistons, not the volume of refrigerant pumped.

  4. #4
    Join Date
    Aug 2010
    Location
    Malta
    Posts
    11
    Rep Power
    0

    Re: Displacement

    Ok I know what you mean .So a compressor of 10m3/h discplacment, it is not discplacing 100m/3 hour, but yes it pumping a volume of 100Nm3/h if the gas is entering in the cylinder at pressure of 10 bar is correct like this ????

  5. #5
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Displacement

    No. The pistons are sweeping 100m3/h, but the actual Nm3/h depends on the volumetric efficiency which is unknown and depends on the pressure drops of valves and manifolds...

  6. #6
    Join Date
    Aug 2010
    Location
    Malta
    Posts
    11
    Rep Power
    0

    Re: Displacement

    Ok got it !!!

    Thanks a lot
    Marco

Similar Threads

  1. who can tell me YORK RXF-101&RXF-24 displacement?
    By joanna in forum Industrial Compressors
    Replies: 4
    Last Post: 21-01-2010, 03:26 PM
  2. Replies: 3
    Last Post: 26-08-2009, 09:37 AM
  3. Chinese Compressors Displacement
    By GRM in forum Technical Discussions
    Replies: 6
    Last Post: 29-06-2009, 08:03 AM
  4. displacement compressors
    By coolhibby1875 in forum Technical Speculations
    Replies: 2
    Last Post: 29-05-2007, 08:11 PM
  5. Compressor Displacement
    By David PS in forum Fundamentals
    Replies: 23
    Last Post: 28-06-2004, 03:43 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •