    leak detector



    Hi all, I really need to find a leak. I'm having problems with finding this particular leak on a VRV system. I have just started to pressure test this for tighteness but before we can get that we need to evaluate where the leak is.
    I've tried listening and going over bubble test at the flares, but theres some hidden pipe brazes above plasterboard ceilings I cant get to yet.
    What I need is a cost for an ultrasonic leak detector if any body knows a good one recently purchased.
    Its either that or using trace helium or hydrogen with OFN & getting a detector for these gases specific to trace. I know this system dropped 10bar over night & its a 'Mare' to find the leak.
    Who knows that if using the ultra sonic one will direct me to the area quicker? before I have to cut out the ceiling to get at the joints to locate?
    Any help appreciated
    Regards Dellapureneed



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: leak detector

    You could rent one for this one-off job perhaps?

    http://www.ashtead-technology.com/uk...ltrasonic+leak
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2007
    Location
    manchester
    Age
    50
    Posts
    5,639
    Rep Power
    45

    Re: leak detector

    split the system and pressure test with helium and nitrogen ie condenser only,then pipework to bc box then each branch to indoor units-get flare plugs and get loads of leak spray- 90% of the time its valve caps on the oudoor unit or bc valves or a cracked flare. 10bar overnight should be easy to find as there should be oil stains! good luck

  4. #4
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: leak detector

    Quote Originally Posted by install monkey View Post
    split the system and pressure test with helium and nitrogen ie condenser only,then pipework to bc box then each branch to indoor units-get flare plugs and get loads of leak spray- 90% of the time its valve caps on the oudoor unit or bc valves or a cracked flare. 10bar overnight should be easy to find as there should be oil stains! good luck

    Seems to be the sensible way, logically isolate and do a drop test on sections of the system. Split the system into near 50:50, then test and proceed by process of ellimination. Then split the faulted section again into 50:50 and so on. Much quicker than tracing around the whole system.

    good luck.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  5. #5
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: leak detector

    Also: Moral of the story - always pressure test before hidden pipework is hidden.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  6. #6
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: leak detector

    I know this wont help you out much ,but i have found on large vrv/vrf installations the best course of action is to test as you go,ie. if you have a system split across floors for example test each floor before connecting to the main line on three pipe systems and on two pipe systems such as mitsu test main line before connecting to bc/indoors.
    A 10bar drop over night is a big leak,,try access the site out of hours . less bodies = less noise
    Might have a better chance of hearing it.
    If it's a new install there wont be any oil stains !!
    Best of luck
    Stu
    Last edited by stufus; 04-01-2011 at 10:54 PM.
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

Similar Threads

  1. Electronic leak detector
    By langy in forum Air Conditioning
    Replies: 7
    Last Post: 27-08-2010, 01:10 PM
  2. Fieldpiece Leak Detector
    By Bones in forum Refrigerants
    Replies: 5
    Last Post: 05-09-2009, 04:49 AM
  3. USX Ultrasonic Leak Detector advice
    By rick19821982 in forum Tools and Calculators
    Replies: 3
    Last Post: 24-06-2009, 08:43 PM
  4. fieldpiece leak detector
    By richelli in forum Tools and Calculators
    Replies: 3
    Last Post: 02-07-2008, 11:44 PM
  5. Tiff 5000 leak detector
    By davidchesson in forum Tools and Calculators
    Replies: 6
    Last Post: 06-11-2006, 04:26 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •