Results 1 to 7 of 7
  1. #1
    Join Date
    Apr 2010
    Location
    australia
    Age
    45
    Posts
    78
    Rep Power
    15

    fujitsu alarm code help?



    hi guys iam a commercial refrigeration mechanic. i will be honest i have never worked on these inverter system. i have a good customer who is have trouble with an a/c. Its a AST30pra. Fujitsu have been out 3 times and cant fix it. i can tell you that there is gas in the system and that one light stays on and the timer light flashes 10 times. any help would be useful.



  2. #2
    Join Date
    Feb 2009
    Location
    England
    Age
    59
    Posts
    9
    Rep Power
    0

    Re: fujitsu alarm code help?

    Hi, try contacting Fujitsu in UK. They may have a diagnostic tell tale on what those lights sequence are.
    Inverters are sensitive to power failures, have you had power cut outs? try a power down/power up reset. You could have a dodgy inverter power board or There may be an overcurrent sensing on compresser start up or maybe the fan if that is also an inverter driven fan. These type of faults tend to lock out the system but reset on power down/up & untill it re senses on start up.

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,712
    Rep Power
    46

    Re: fujitsu alarm code help?

    Try reading the attached.
    It may help you resolve your issue, although they don't list 10 flashes?

    Good Luck
    Grizzly

    http://www.refrigeration-engineer.co...ad.php?t=21050

  4. #4
    Join Date
    Feb 2008
    Location
    england
    Posts
    502
    Rep Power
    21

    Re: fujitsu alarm code help?

    10 flashes ipm error
    Abnormal current value of IPM is detected > Permanent stop. Heat radiation is blocked (inlet/outlet).
    -Check if outdoor fan is defective (does not rotate).
    -Controller PCB defective (refer to IPM diagnosis).
    -Refrigeration cycle defective (refer to refrigeration troubleshooting

  5. #5
    Join Date
    Feb 2008
    Location
    england
    Posts
    502
    Rep Power
    21

    Re: fujitsu alarm code help?


  6. #6
    Join Date
    Apr 2010
    Location
    australia
    Age
    45
    Posts
    78
    Rep Power
    15

    Re: fujitsu alarm code help?

    Thanks for your help guys. I will try the condenser fan. If fujitsu cant fix it with all their service manuals i surely have no chance.

  7. #7
    Join Date
    Dec 2010
    Location
    devon
    Age
    53
    Posts
    837
    Rep Power
    24

    Re: fujitsu alarm code help?

    check the thermistors on outdoor they control the fan and control circuit they are extremley prone to failure however they usually bring a code on indoor when the two buttons are pressed be lucky charlie

Similar Threads

  1. Carrier Transicold Container Problem
    By Shamel in forum Transport
    Replies: 39
    Last Post: 23-01-2012, 11:23 PM
  2. Fujitsu Error Code 00:2F
    By ejrampe in forum Trouble Shooting
    Replies: 3
    Last Post: 06-01-2011, 05:44 AM
  3. Fujitsu ASTA34LCC Fault Code
    By ckw_79 in forum Technical Discussions
    Replies: 0
    Last Post: 04-05-2010, 12:43 AM
  4. Fujitsu Error Code E0:17
    By krisbendeich in forum Trouble Shooting
    Replies: 3
    Last Post: 04-11-2009, 12:49 AM
  5. Fujitsu ASTA09LCC error code
    By exotiic in forum Air Conditioning
    Replies: 9
    Last Post: 19-08-2009, 03:56 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •