    5 ton kws



    Did a power consumption reading on a 5 ton, single phase, A/C unit and the total power consumption for the Evap and condenser was 4.36kw. Is this reading normal?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    75
    Posts
    11,192
    Rep Power
    60

    Re: 5 ton kws

    Sorry, don't know.

    What does the data plate on the unit say?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Jun 2010
    Location
    Belize
    Posts
    11
    Rep Power
    0

    Re: 5 ton kws

    there is no refrence to the power consumption , but its a five ton single , 208 volts unit, compressor running and evap fan on high

  4. #4
    Join Date
    Nov 2010
    Location
    London
    Posts
    625
    Rep Power
    15

    Re: 5 ton kws

    Quote Originally Posted by ostaine View Post
    Did a power consumption reading on a 5 ton, single phase, A/C unit and the total power consumption for the Evap and condenser was 4.36kw. Is this reading normal?
    Sounds about right - the unit is probably not running at design full load. The numbers are about where we would expect them to be with the unit running say 70 to 80% Loaded - meaning the return air and outdoor air enthalpy's are low enough to, in a combined fashion, amount to less that full design load conditions.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  5. #5
    Join Date
    Jun 2010
    Location
    Belize
    Posts
    11
    Rep Power
    0

    Re: 5 ton kws

    Waiting for a warm day to do recording of with reps from utility company using Fluke test gear. will also record ambient and room temp

  6. #6
    Join Date
    Jun 2010
    Location
    Belize
    Posts
    11
    Rep Power
    0

    Re: 5 ton kws

    single 5ton a/c , compressor running, condenser fan running, evap fan on high,
    Ambient 88.5 F
    Power consumption 4.352 Kw
    Room Temp 71.6 F

  7. #7
    Join Date
    Jun 2010
    Location
    Belize
    Posts
    11
    Rep Power
    0

    Re: 5 ton kws

    Here's what on the nameplates.
    Condensing Unit
    Make : Goodman
    Model : CKL60 - 1L
    A/C Volts : 208/230 phase 1 Hertzs 60
    Factory Charge oz R22 115
    COMPRESSOR
    Make : Copeland ZR57KC-PFV-250
    RLA 25 A LRA 150
    Evaporator
    Model #UG060CKA2LACL2
    SERIAL # 50050072-4118

  8. #8
    Join Date
    Jun 2010
    Location
    Belize
    Posts
    11
    Rep Power
    0

    Re: 5 ton kws

    Here's what on the nameplates.
    Condensing Unit
    Make : Goodman
    Model : CKL60 - 1L
    A/C Volts : 208/230 phase 1 Hertzs 60
    Factory Charge oz R22 115
    COMPRESSOR
    Make : Copeland ZR57KC-PFV-250
    RLA 25 A LRA 150
    Evaporator
    Model #UG060CKA2LACL2
    SERIAL # 50050072-4118