    Cool nitrogen vs. ***** r22 vs. ???



    good day ya all !

    i'm new at this forum, but i was following threads for awhile now ..

    and now, i have a serious question, hope someone could help !


    in my company, we are using ***** r22 to detect leakage in condenser soils, pressurized up to 100 psi. then we add nitrogen gas to increase the net pressure up to 450 psi.

    then we sealed it, and use ***** r22 detector to investigate for leaks with sensitivity of 0.01 oz/yr.


    now, i'm thinking of replace the current system by only using nitrogen gas, which we already generate in house, as testing gas, and we also might install some recovery system to re-use the nitrogen number of times. where we also going to test some units at 650 psi.

    my question is, is there a nitrogen detector that can detect leaked nitrogen gas of sensitives 0.01 oz/yr ?

    if not, what would be an alternative gas for testing, and what is the best detection system for the alternative gas ?


    thanx and happy new year to ya all !




  2. #2
    Join Date
    Jan 2011
    Location
    Saudi Arabia
    Posts
    6
    Rep Power
    0

    Re: nitrogen vs. ***** r22 vs. ???

    condenser coils * << spelling mistake

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: nitrogen vs. ***** r22 vs. ???

    Hi Eddi,

    There is a lot of nitrogen in the air so a detector won't be able to tell the difference between background nitrogen and any that may have leaked from the system being tested.

    I believe a lot of manufacturers test with nitrogen with a trace of helium (it is available ready mixed here) as helium is not generally found in the air and has very small molecules so is good at finding very small leaks. Special helium detectors are needed.

    Jon

  4. #4
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: nitrogen vs. ***** r22 vs. ???

    I have a Dtec select detector and that picks up Nitrogen. As I only work on smaller refrigeraton systems these days with short pipe runs (less than 20 meters). I can always use leak detection spray if the leak isn't local or doesn't trace on the detector. Over here in Europe its illegal to vent ***** into the atmosphere, or even top up a leaking system with *****. Do you have a similar EPA/F gas regs implemented in Saudi?

    edit

    Or there's always the UV tracing die, I never used though so I don't know if its any good or not.
    Last edited by chilliwilly; 01-01-2011 at 01:34 PM. Reason: missing text.

  5. #5
    Join Date
    Jan 2011
    Location
    Saudi Arabia
    Posts
    6
    Rep Power
    0

    Re: nitrogen vs. ***** r22 vs. ???

    i liked your idea ..

    and i missed that point of background nitrogen .. it really matters

    anyhow, can you provide me with more detail about the nitrogen-helium gas .. like the vendor or pricing or even if you have tried it and you have some more details

    thanx in advanced

  6. #6
    Join Date
    Jan 2011
    Location
    Saudi Arabia
    Posts
    6
    Rep Power
    0

    Re: nitrogen vs. ***** r22 vs. ???

    Quote Originally Posted by chilliwilly View Post
    I have a Dtec select detector and that picks up Nitrogen. As I only work on smaller refrigeraton systems these days with short pipe runs (less than 20 meters). I can always use leak detection spray if the leak isn't local or doesn't trace on the detector. Over here in Europe its illegal to vent ***** into the atmosphere, or even top up a leaking system with *****. Do you have a similar EPA/F gas regs implemented in Saudi?

    edit

    Or there's always the UV tracing die, I never used though so I don't know if its any good or not.
    thanx for your reply

    so far, no regulation has taken place, but soon it will be.

    i will check the UV, knowing though it's not the best solution for the company. thanx anyway

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: nitrogen vs. ***** r22 vs. ???

    One other option to consider is using an ultrasonic leak detector. No need to use a trace gas and will work with OFN

    http://www.inficonultrasonicleakdete...kdetector.html

    http://www.refrigeration-engineer.co...ght=ultrasonic
    Last edited by frank; 01-01-2011 at 03:16 PM.

  8. #8
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: nitrogen vs. ***** r22 vs. ???

    You can add a small amount of Helium to the Nitrogen.
    helium is easier to detect and you can detect smaller leaks.

  9. #9
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: nitrogen vs. ***** r22 vs. ???

    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  10. #10
    Join Date
    Jan 2011
    Location
    Saudi Arabia
    Posts
    6
    Rep Power
    0

    Re: nitrogen vs. ***** r22 vs. ???

    thank you all

    actually i started working in your ideas, specially the nitrogen-helium mix and the UV.

    but so far the best sensitivity UV offers is 0.1 oz/yr, while we strictly require 0.01 oz/yr for best quality.

    thus, i'm thinking more about the traced gas mixture.


    thanx for your help guys

    i'll dig more and hopefully i'll find a way.

  11. #11
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: nitrogen vs. ***** r22 vs. ???

    Why so high test pressures,,,,are these CO2 systems?
    450 psi and 650 psi oh my god.
    Remember we are here for a good time, not a long time.
    Trust me i'm a Fridgy.

  12. #12
    Join Date
    Jan 2011
    Location
    Saudi Arabia
    Posts
    6
    Rep Power
    0

    Re: nitrogen vs. ***** r22 vs. ???

    they're chiller condenser coils and evaporators

    the testing for cond. coil is done at 450 psi, evaporator at 350 psi.

    the 650 psi is for upcoming bigger units.

    and as you know, testing should be conducted at the operating limits. it's not just an exaggeration of higher standards.

  13. #13
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: nitrogen vs. ***** r22 vs. ???

    Safe handling of refrigerants states that pressure testing shall be:-

    for Strength 1.1 - 1.43 MWP for a minimum of 15 mins
    For leak detection 1 x MWP for minimum 60 mins

    Mwp = 55c Air cooled high side, 43c Water cooled high side and 32c low side

    I use 1.1 for strength then leak test at 1 x MWP

  14. #14
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: nitrogen vs. ***** r22 vs. ???

    Quote Originally Posted by SkyWalker View Post
    Safe handling of refrigerants states that pressure testing shall be:-

    for Strength 1.1 - 1.43 MWP for a minimum of 15 mins
    For leak detection 1 x MWP for minimum 60 mins

    Mwp = 55c Air cooled high side, 43c Water cooled high side and 32c low side



    I use 1.1 for strength then leak test at 1 x MWP
    It s BS EN 378 2008 which states that not safe handling of refrigerants
    Last edited by Brian_UK; 03-03-2011 at 10:13 PM. Reason: Tidy up quotation

  15. #15
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: nitrogen vs. ***** r22 vs. ???

    Also, if within the EU then using refrigerant for leak testing is illegal.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  16. #16
    Join Date
    Aug 2007
    Location
    Sydney
    Age
    51
    Posts
    1,083
    Rep Power
    23

    Re: nitrogen vs. ***** r22 vs. ???

    Eddi
    In the old days when we couldn't find a leak on a coil but knew there was one we would remove the coil blow it up with nitro and submerse it into a bucket of water and see bubbles where the leaks were. But I'm not sure what rate of detection this method would give. Just a thought but I think the Helium and ultrasonic ideas are better.

  17. #17
    Join Date
    Nov 2006
    Location
    At home
    Posts
    181
    Rep Power
    18

    Re: nitrogen vs. ***** r22 vs. ???

    Quote Originally Posted by Quality View Post
    It s BS EN 378 2008 which states that not safe handling of refrigerants

    fair enough, u know what i mean its doing it correctly thats important

  18. #18
    Join Date
    Dec 2008
    Location
    UK
    Posts
    564
    Rep Power
    24

    Re: nitrogen vs. ***** r22 vs. ???

    There is also the nitrogen/hydrogen mix that is available. You will need a special leak detector and normally do not need to test at such high pressures to find a leak. It is quite expensive if used in large quantities and may not suit your manufacturing test pressures.
    Mobile A/C at its best, see avatar.
    Bedford. Now retired and trying to relax.

  19. #19
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: nitrogen vs. ***** r22 vs. ???

    Quote Originally Posted by SkyWalker View Post
    fair enough, u know what i mean its doing it correctly thats important
    Yeh I know what ya mean, I posted so that everyone else does.

  20. #20
    tajger's Avatar
    tajger Guest

    Re: nitrogen vs. ***** r22 vs. ???

    Use nitrogen and submerge the condenser in a pool.

Similar Threads

  1. Dupont line size calculator also has 410a and 407c
    By 128cyclist in forum Tools and Calculators
    Replies: 6
    Last Post: 20-08-2009, 03:45 PM
  2. Water in *****
    By chemi-cool in forum Refrigerants
    Replies: 47
    Last Post: 17-08-2009, 10:16 PM
  3. Nitrogen Condensing by Temperarture
    By Reflexive in forum Technical Discussions
    Replies: 0
    Last Post: 21-12-2008, 12:23 AM
  4. Water in *****
    By Tycho in forum Hydrocarbons
    Replies: 5
    Last Post: 27-05-2008, 06:45 PM
  5. ***** and memory lapse
    By Tycho in forum Fundamentals
    Replies: 11
    Last Post: 30-01-2007, 11:17 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •