    Re: Home made swimming pool heat pump



    Quote Originally Posted by frank View Post
    Have you fitted a TEV yet or are you still trying to make it work with the capillary?
    Ok, just watched a video on TXV's and their construction. Looks like it'll be an interesting addition. So, as usual some questions;

    1. What rating of TXV do I need
    2. Do I need one that has the ability to be externally equalized
    3. At what point on the suction line does the bulb need to be placed.
    4. How do I attach the bulb, a jubilee clip/tie wraps/tape?

    Thanks to all!

    Nigel



  2. #102
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    Ok, just watched a video on TXV's and their construction. Looks like it'll be an interesting addition. So, as usual some questions;

    1. What rating of TXV do I need
    2. Do I need one that has the ability to be externally equalized
    3. At what point on the suction line does the bulb need to be placed.
    4. How do I attach the bulb, a jubilee clip/tie wraps/tape?

    Thanks to all!

    Nigel
    1. I'd base the TXV capacity on the cooling duty of the original air con system.
    2. Externally equalised would be best.
    3. Just after the outlet of the evaporator. The equalising line is piped to just after the bulb.
    4. The valve should come complete with a clamp, but a jubilee clip will get you going. The bulb needs to be insulated too.

    Most TXV's have an instruction sheet in the box or printed on the box itself.

    Jon

  3. #103
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    Copper in chlorinated water. I've put a spare bit of tube in the filter basket on my pool pump which has to be one of the most volatile places for a tube to be as it has no chance of forming an oxide layer to protect itself from corrosion. So far no change, no degredation, it hasn't even lost its dullness which would be a sure sign of corrosion. I'm going to keep it in there just in case!

    The clean copper in your system could also be due to the water scouring the metal and slowly erroding it. If the Ph is low, say less than 0.7 there will be a tendancy for the water to leech metal components. Hence shiny copper.

    Oxide layers that form on copper in pool atmospheres are usually "Verdi Gris" which does not provide a protective layer. Over time pin hole penetration will occure, and with the refrig pipework, oil will slowly weep through causing the verdis gris to become pasty to touch.

    On another note, There is now a following of operators using Copper ionisation in the pool water instead of chlorine. I believe it's a cheaper method. I have no invormation but yuo can search and find many sites that sell this product.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  4. #104
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: Home made swimming pool heat pump

    Quote Originally Posted by monkey spanners View Post
    1. I'd base the TXV capacity on the cooling duty of the original air con system.
    I've no idea what that was, there is no label or anything. Only the model number and initial charge. The compressor is 3Kw and a COP of 3 so what would I expect, 9Kw cooling? From the video they talked about 'tonnes', how does this relate? What measurement do TXV's come in? Kw/Tonnes/something else?

  5. #105
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by frank View Post
    Some years back, a friend asked me to have alook at his fathers pool heater.

    A basic set up with a condensing unit, maybe 1hp, situated within his large green house and a stainless steel cylinder with copper discharge pipework coil running through it. It looked like a home made jobby.

    When I connected my gauges on the suction rotolock, water came out

    When It was stripped in our workshop, the discharge copper coil was disintegrating,

    I managed to replace it, dry out the existing condenser, rebuild it and re-install it back into his greenhouse. It's still going strong

    I used 316 S/S tubing though, not copper in the re-build.

    I haven't worked on any S & T HX's for pools since, only brazed plate HX's
    I have come across many situations simillar to that you mention. We find if we test the water the PH tends to be down below 0.7. At this level the water leeches all metal components. In some cases I've had to return and redo the whole wash out within months of the first repair. One guy was an industrial chemist and thought checking his water 6 monthly would be adequate? every week is essential at the min.

    I find worse case is when there are lots of children using the pool for other than swimming. Air born Chloramines rot all the metal work, stainless as well.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  6. #106
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    I've no idea what that was, there is no label or anything. Only the model number and initial charge. The compressor is 3Kw and a COP of 3 so what would I expect, 9Kw cooling? From the video they talked about 'tonnes', how does this relate? What measurement do TXV's come in? Kw/Tonnes/something else?
    A ton is 12000 btu is 3.5Kw.

    Whats the model no. and make of your unit?

    What make of expansion valve did they have at the wholesalers?

  7. #107
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    Sounds like it to me - according to nobility table stainless steel is quite anodic and far away from copper which is cathodic with the result being that the copper will corrode.
    There is always that possibility but the majority of corrosion in swim pool apps is not due to electrolytic wasting but chemical reaction. That's why it is essential the chemical balance of the water is kept spot on.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  8. #108
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: Home made swimming pool heat pump

    Quote Originally Posted by monkey spanners View Post
    Whats the model no. and make of your unit?

    What make of expansion valve did they have at the wholesalers?
    Fujitsu AOG25AWNL. Tecumseh AW5532A compressor.

    I can't remember the make of the valves, they only had one make so little choice!

  9. #109
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: Home made swimming pool heat pump

    Ok, went to the wholesalers to ask what they had. The units they sell are Danfoss TX2 devices. He asked which one and I had no idea! So, over to you guys!

  10. #110
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Home made swimming pool heat pump

    Your unit is rated at 7.2Kw nominal cooling so your TEX2-(N) needs to be externally equalised with a No.4 orifice (8Kw nominal)

    The valve body is the DAN112. The orifice is a DAN208.
    The valve will have 3/8" and 1/2" flare connections. The equalising port will have a 1/4" flare connection.
    Do you have a flaring tool?

    Don't buy the TX2 as this is internally equalised

  11. #111
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: Home made swimming pool heat pump

    Yes, have a flaring tool so no problem. Will go and see if they have this one in stock in the morning and get it installed if they do.

    Work interrupted pleasure today so I'll be building the second heat exchanger tomorrow. Have the unit turned off at the moment as I don't want to damage the compressor with excessive heat.

    Beautiful sunny weather here at the moment so the solar panels are working hard.

  12. #112
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: Home made swimming pool heat pump

    Quote Originally Posted by frank View Post
    Your unit is rated at 7.2Kw nominal cooling so your TEX2-(N) needs to be externally equalised with a No.4 orifice (8Kw nominal)

    The valve body is the DAN112. The orifice is a DAN208.
    The valve will have 3/8" and 1/2" flare connections. The equalising port will have a 1/4" flare connection.
    Do you have a flaring tool?

    Don't buy the TX2 as this is internally equalised
    What part numbers? There are several, I can't find any that has a reference of DAN112 or DAN208, the orifice I guess is part 68-2007.
    http://www.kulde.org/CH8/TE2.pdf

    Thanks!

  13. #113
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    Just bought the bits to make the second condenser so will hopefully make it tomorrow. Still using a capillary but my suppliers have TXV's so will get one and try to work out how to install it. I guess it replaces the capillary, the one he showed me had 2 ports, what looked to be a point to adjust it and what looked like a bulb on the end of a thin coil. Where does this go?
    Nigel

    Based on your compressor model. The compressor duty at
    4.5 barg suction
    18 barg disch
    has a duty 7.8kW. R22

    Expansion valve required
    Danfoss TEX2N (without MOP) has duty of 8.9 kW with press drop of 10 b evap at 5C. when using orifice No 03.
    As you're able to braze then the better option of valve would be one you can braze into the sytem.

    TEXN part number 068Z328400 (solder)
    plus
    Orifice 03 Part number 068 209300
    plus 3/8 solder adaptor 068 206066


    There is a 25% leaway with these valves on their duty and of course you may need to adjust the superheat once up and running.

    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  14. #114
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by frank View Post
    Your unit is rated at 7.2Kw nominal cooling so your TEX2-(N) needs to be externally equalised with a No.4 orifice (8Kw nominal)

    The valve body is the DAN112. The orifice is a DAN208.
    The valve will have 3/8" and 1/2" flare connections. The equalising port will have a 1/4" flare connection.
    Do you have a flaring tool?

    Don't buy the TX2 as this is internally equalised

    Sorry to butt in here Frank.
    I think you may be quoting nominal duty for the orifice wich is only based on a 2 bar dp across the valve. this application is most likely to have 10 bar dp across the valve. in that case an orifice No. 03 would be most suited as it's duty is 8.9 kW Whereas the no.04 orifice will have a duty of 13.3 kW ... too high I think.
    Last edited by nevgee; 05-02-2011 at 11:29 AM. Reason: typo correction
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  15. #115
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  16. #116
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    What part numbers? There are several, I can't find any that has a reference of DAN112 or DAN208, the orifice I guess is part 68-2007.

    Thanks!
    See above post
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  17. #117
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    This link may be helpfull ... Danfoss "Fitters notes" gives instructions on Expansion valves and setting them up.

    http://ra.danfoss.com/TechnicalInfo/...chapter_01.pdf
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  18. #118
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by MikeHolm View Post
    Parallel, pipe it is parallel. I would think the pressure drop is important. Des, Gary?

    I think you're quite right here. Does Acuario have the necessary information to pipe up the second condenser, taking into consideration the gas flows to ensure even balancing and equal flow through both condensers?
    Perhaps someone has got some typical pipework arrangements that he could follow. Otherwise I fear he may hook up the 2nd condenser and find his gas flows are wrong.

    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  19. #119
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Attached Danfoss pages with TEX selection data
    Attached Files Attached Files
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  20. #120
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Home made swimming pool heat pump

    I was using the RPW Catalogue

  21. #121
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by frank View Post
    I was using the RPW Catalogue

    Maybe you need to refresh your glass and try different brew?
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  22. #122
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: Home made swimming pool heat pump

    Well I opted for Heat Exchanger MKII instead of a second MKI in parallel, I could always parallel them up if necessary.

    MKII has more coils; 3 to be precise, coil 1 wound on a 32mm former, coil 2 wound on a 50mm former and coil 3 wound on a 75mm former. All then fitted one inside the other and linked at either end. The pipe in each coil is 1/4" diameter. Coil 1 is about 6m long, coil 2 about 9m long and coil 3 about 15m long (now you're going to tell me they should all be the same!).

    They are all contained in a 110mm diameter pipe 68cm long.

    As I write I'm waiting for the glue to finish drying. I'll post pictures later.

    My supplier isn't open saturday afternoons so I'll go and order/purchase the TXV on monday.

  23. #123
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    Well I opted for Heat Exchanger MKII instead of a second MKI in parallel, I could always parallel them up if necessary.

    MKII has more coils; 3 to be precise, coil 1 wound on a 32mm former, coil 2 wound on a 50mm former and coil 3 wound on a 75mm former. All then fitted one inside the other and linked at either end. The pipe in each coil is 1/4" diameter. Coil 1 is about 6m long, coil 2 about 9m long and coil 3 about 15m long (now you're going to tell me they should all be the same!).


    Ideally, yes. You really need to try to ensure the gas flows are equal through the sections of the condenser.

    Had you not considered using a tank instead of a pipe to contain the coils?
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  24. #124
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by nevgee View Post
    I have come across many situations simillar to that you mention. We find if we test the water the PH tends to be down below 0.7. At this level the water leeches all metal components. In some cases I've had to return and redo the whole wash out within months of the first repair. .
    Sorry for my error ..... should have read 7.0 not 0.7.

    The ph of a swimpool water should ideally be 7.4
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  25. #125
    Join Date
    Dec 2010
    Location
    Toronto, Canada
    Age
    60
    Posts
    1,454
    Rep Power
    24

    Re: Home made swimming pool heat pump

    If you are able to ensure roughly even flow over each of the coils, they should be of roughly equal lengths of tubing although, I believe, the coil with a larger helical diameter will have a slightly smaller pressure drop.

  26. #126
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: Home made swimming pool heat pump

    Here we go again, a disaster, bad weather and work got in the way but at last I'm off again..
    The disaster - I managed to leave a small unbrazed hole in HX MKII and flooded my evaporator etc . I also managed to dump my charge of R22 into the pool at the same time . So, a change of refrigerant and a bit of a clean up was in order..
    Blew everything out with Nitrogen and it is up and seems to be running again. As there was no refrigerant left, and I was concerned about any moisture in the compressor (I'm sure there was) I added a filter dryer and at the same time cut out the capillary and installed a TXV.

    The TXV is a Danfoss TX2, 068Z3206 and I fitted orifice No. 03, but without filter as that was all he had.

    So, it's running again with a new refrigerant, RS44 (R424A), slightly different PT characteristics but it's a drop in replacement.

    Measurements are (fan at full speed):
    Compressor exit temperature: 53.5'C
    Pressure 112psig
    Condensor entry 53.1'C
    Condensor exit 16'C
    TXV entry 14'C
    TXV exit (evaporator entry) -1.8'C
    Evaporator exit 5.9'C
    Suction pressure 37psig

    Tuning advice welcome!

    Nigel

  27. #127
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    Here we go again, a disaster, bad weather and work got in the way but at last I'm off again..
    The disaster - I managed to leave a small unbrazed hole in HX MKII and flooded my evaporator etc . I also managed to dump my charge of R22 into the pool at the same time . So, a change of refrigerant and a bit of a clean up was in order..
    Blew everything out with Nitrogen and it is up and seems to be running again. As there was no refrigerant left, and I was concerned about any moisture in the compressor (I'm sure there was) I added a filter dryer and at the same time cut out the capillary and installed a TXV.

    The TXV is a Danfoss TX2, 068Z3206 and I fitted orifice No. 03, but without filter as that was all he had.

    So, it's running again with a new refrigerant, RS44 (R424A), slightly different PT characteristics but it's a drop in replacement.

    Measurements are (fan at full speed):
    Compressor exit temperature: 53.5'C
    Pressure 112psig
    Condensor entry 53.1'C
    Condensor exit 16'C
    TXV entry 14'C
    TXV exit (evaporator entry) -1.8'C
    Evaporator exit 5.9'C
    Suction pressure 37psig

    Tuning advice welcome!

    Nigel
    112 psig for R22 (from P/T chart) is about 19C-16C (exit temp) =3K subcooling. Add refrigerant slowly until the subcooling is about 8.5K.
    Last edited by Gary; 05-03-2011 at 12:23 PM.

  28. #128
    Join Date
    Dec 2010
    Location
    Spain
    Posts
    46
    Rep Power
    0

    Re: Home made swimming pool heat pump

    I had a small leak so had to remove the gas, fix it and re-gas. Obviously readings changed...
    I also spotted I put a wrong value - too many scribbles on my bit of paper!
    A new bit of paper so no confusion!
    Readings are:

    Ambient: 15'C
    Water: 20'C
    Exit pressure: 167psig
    Exit temp: 64'C
    Condensor entry: 61'C
    Condensor exit: 26'C
    Evap exit: 11'C
    Suction pressure: 38psig

    So, following the above I have subcooling:
    32.2 - 11 = 21.2K

    Is this too high? Should I try to reduce it?

    Nigel
    Last edited by Acuario; 05-03-2011 at 03:28 PM.

  29. #129
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    I had a small leak so had to remove the gas, fix it and re-gas. Obviously readings changed...
    I also spotted I put a wrong value - too many scribbles on my bit of paper!
    A new bit of paper so no confusion!
    Readings are:

    Ambient: 15'C
    Water: 20'C
    Exit pressure: 167psig
    Exit temp: 64'C
    Condensor entry: 61'C
    Condensor exit: 26'C
    Evap exit: 11'C
    Suction pressure: 38psig

    So, following the above I have subcooling:
    32.2 - 11 = 21.2K

    Is this too high? Should I try to reduce it?

    Nigel
    That's 32C-26C=6K

  30. #130
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Home made swimming pool heat pump

    Quote Originally Posted by Acuario View Post
    I had a small leak so had to remove the gas, fix it and re-gas. Obviously readings changed...
    I also spotted I put a wrong value - too many scribbles on my bit of paper!
    A new bit of paper so no confusion!
    Readings are:

    Ambient: 15'C
    Water: 20'C
    Exit pressure: 167psig
    Exit temp: 64'C
    Condensor entry: 61'C
    Condensor exit: 26'C
    Evap exit: 11'C
    Suction pressure: 38psig

    So, following the above I have subcooling:
    32.2 - 11 = 21.2K

    Is this too high? Should I try to reduce it?

    Nigel
    38psig = 2.6 barg = -9C sst Too low
    super heat -9 -11 = 20C Far too high

    Add gas as Gary suggests and open TX valve to reduce Sh. approx one full turn counter clockwise will give 4 C .. so 2 to 3 full turns might do the trick. Check instructions on box. Do it at 1 turn at a time and allow 10 - 15 mins for the system to settle down each time.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

Page 3 of 3 FirstFirst 123

Similar Threads

  1. Seeking Tips on Getting the Most from a Heat Pump
    By kenelias in forum New to RE
    Replies: 4
    Last Post: 29-11-2010, 08:52 PM
  2. Pool Heat Pump
    By elvis in forum Heat Pumps
    Replies: 5
    Last Post: 23-03-2010, 09:18 PM
  3. Capacity control
    By sparrow in forum Training
    Replies: 44
    Last Post: 18-01-2010, 07:49 PM
  4. Home designed and built heat pump!
    By The MG Pony in forum Heat Pumps
    Replies: 15
    Last Post: 17-08-2007, 02:01 AM
  5. Heat pump made from a TM-15HD?
    By The MG Pony in forum Transport
    Replies: 8
    Last Post: 18-05-2007, 07:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •