Results 1 to 45 of 45
Thread: Speed in evaporator tube
31-12-2010, 06:45 AM #1
Someone able to calculate these for me please?
I personally know who can do this - I can't - but i want to make this a general question.
What will be the theoretical speed through an 1/2" line - length 15, 30 and 70 m - of an evaporator, 2 kW, evaporating at 0°C for R410a and R407c, condensing at 35°C and 40°C and a SC of 10K and second case 20K, Sh of 5K?
We start with a saturated gas/liquid mixture in the beginning and ending with a superheated gas.Last edited by Peter_1; 31-12-2010 at 07:13 AM. Reason: Forgot most important data to add
31-12-2010, 06:56 AM #2
Re: Speed in evaporator tube
Keeping with the theme of the question, we are missing some data, to calculate the next stage!
Data can be supplied in a number of ways!!!!!!!
31-12-2010, 07:11 AM #3
Edited, indeed, forgot some data, in fact most important data. Sorry
Reason for my question: a colleague/friend is installing DX heatpumps and he's using for this copper in lengths of 70m. I was suggesting that this is far too long and should be something in the range of 30 m. I say he could have pressure drops of more than 1 bar and he didn't believe this.Last edited by Peter_1; 31-12-2010 at 07:16 AM.
31-12-2010, 07:17 AM #4
31-12-2010, 07:42 AM #5
31-12-2010, 08:13 AM #6
Only 1 straight pipe Aik where the give evaporating pressure is the outlet pressure.
My colleague is now measuring 0°C (converted from pressure of 3.5 bar) for R407c (!) at the compressor inlet and he's thinking that the whole circuit of 14 kW (7 circuits of 2 kW) is evaporating at 0°C.
If there should be no pressure drop, then the whole circuit starts at -6°C (+/-)
Due to a possible pressure drop of 1 bar for R407c, the whole circuit stays at 0°C.
I advised him to reduce his lines to 30 m and that this should benefit the COP of the compressor due to the lower DP over the copper.
If I calculate Dp for a 1/2" line of 70m , R407c for the given conditions, then this gives me 1.2 bar DP (8.7K) for a gas line and a neglectable DP for the 1/2" liquid line.Last edited by Peter_1; 31-12-2010 at 08:18 AM.
31-12-2010, 07:17 AM #7
31-12-2010, 07:20 AM #8
m' = r*Ac*v
Where :
m' = mass flowrate [kg/s]
r = density (vapour, or liquid, or 2-phase) [kg/m3]
Ac = cross-sectional area of pipe (ID-based) [m]
v = velocity [m/s]Engineering Specialist - Cuprobraze, Nocolok, CD Technology
31-12-2010, 07:40 AM #9
Carrying on now we have more data,
your evaporating pressure, is this your outlet pressure leaving the pipe.
31-12-2010, 08:00 AM #10
31-12-2010, 08:09 AM #11
So you now need to work out the mass flow of each refrigerant/condition to meet your 2 KW, use PH chart, whilst looking at the chart look up the density of the refrigerant at the pipe exit conditions, then calculate as per DesA formular (maximum velocity/speed)
Or Just use Coolpack !!!!!!!Last edited by mad fridgie; 31-12-2010 at 08:12 AM.
31-12-2010, 08:20 AM #12
The condition of the gas constantly changes while the refrigerant flows from the beginning to the end of the pipe. So I think we just can't assume outlet nor inlet conditions to calculate speed in this line. It's somehow an mathematical expression that needs to be used.
31-12-2010, 08:39 AM #13
At those conditions the speed at the exit will remain constant (for each refrigerant and set of conditions)
Your speed will increase from the start to the end, due to change in density.
Have you worked out the amount of of surface area you require,
So if I understand it correctly, you have 7 circuits at 70 meters, you want lets say 14 circuits at 35 meters (same surface area, reduced pressure drop) but could reduced refrigerant heat transfer co-efficient
31-12-2010, 08:57 AM #14
Q=m'*dH - capacity [kW]
m' - mass flowrate [kg/s]
dH - difference of enthalpies of evaporating and suction refrigerant [kJ/kg]
Acording to this formula you can calculate m'. After with help DesA's formula you can calculate velocity. Entalpy you can find using CoolPack.
dP=lamda*(l/d)*(r*v^2)/2 - pressure drop on straight tube [Pa]
lamda - friction coefficient, for copper tubes lamda=0.03
l - tube's length [m]
d - inner diameter of tube [m]
r - density (vapour, or liquid, or 2-phase) [kg/m3]
v - velocity [m/s]
P.S. for more accuracy for 10^5< Re < 10^8
lamda=0.0032+(0.221/(Re^0.237))
Re - Reynolds numberLast edited by Aik; 31-12-2010 at 09:40 AM. Reason: correction spelling errors
In some places will have to think ...
31-12-2010, 01:20 PM #15
I can calculate it manually with the refrigerant properties out of saturated tables or superheated valeus via the log p/h but then I'm starting with conditions which doesn't change that much while transporting the gas or liquid along the lines.
In the evaporator tubes, we have a very rapid and intense phase change an a huge expanding of the liquid to its gaseous state. So the characteristics changes continuously along the line of 70 m.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
31-12-2010, 09:17 AM #16
See Spread Sheet attached in message further down the thread....
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
31-12-2010, 02:13 PM #17
31-12-2010, 02:45 PM #18
DTLArca, Where can I find different viscosities of refrigerant at different conditions?
In attachment what I calculated but don't know if it's correct 85 kPa pressure drop.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
31-12-2010, 04:36 PM #19
Happy New Year.
http://www.solvay-fluor.com/docroot/...s/download.htmIn some places will have to think ...
31-12-2010, 07:13 PM #20
31-12-2010, 10:06 PM #21
I think you have used a vapour density 1/10th of what it actually will be, so, your vapour velocity is of course 10 times faster than it actually will be. I get a total pressure drop of 0.2Bar along the 70m. Your liquid calcs look okay though. Have a look at the modified spread sheet attached...
There are 4 sheets now:- Copper Tube Dimension Choices
- Refrigerant and tube values converted to velocity if all liquid and then again velocity if all vapour and thereafter, based on average X (kg/kg) values for each 5th pipe length, a total pressure drop is calculated based on the implied proportions of liquid versus vapour.
- R410A values
- R407C values.
Last edited by DTLarca; 31-12-2010 at 10:17 PM. Reason: Edited mm to m in spread sheet then re-uploaded spread sheet.
01-01-2011, 10:11 PM #22
I think DTLarca enlightened a little bit my confusion. The entire length of 70 m was divided in 5 different sections where in each section we have each time a new 'mixture' due to the ever increasing gas phase (and decreasing liquid phase) of the refrigerant along the copper tube.
But, I see a big difference between DTLarca and desA. I think I will make a practical setup for this and test this once.Last edited by Peter_1; 01-01-2011 at 10:13 PM.
31-12-2010, 01:46 PM #23
A gift for Peter. Happy New Year for 2011.
'Natural' circuit. 3c.
7c. 2 unlinked tubes.
14c. 2 unlinked tubes.
'Natural' circuit. 19c.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
31-12-2010, 02:11 PM #24
desA, first of all, thanks for your help - as usual. For you and all the other colleagues, a Happy NewYear (in some parts of the world, it's already Newyear I guess)
desA, Let's take your coil consisting of 7 tubes, where the total coil DP is 7.66 kPa (or 0.076 bar...I'm used to work with bar)
Because the total pressure = 1/partial pressure losses (like a parallel connection of electrical resistances), can I then say that the DP over 1 tube of the coil is then 7 times 7.66 kPa or 53.62kPa (= 0.53 bar)?
Splitting the same capacity over 14 circuits reduces the DP with a factor of 7.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
31-12-2010, 02:32 PM #25
As a first approximation, we could use the Bernoulli equation across each circuit.
dP,14/dP,7 ~ (Ac,7/Ac,14)^2 = (Ac,7/(2*Ac,7))^2 = 1/4
Backcheck:
dP,14/dP,7 = 0.0696/0.248 = 0.2806 ~ 0.25 = 1/4
The difference probably comes from his bend calculations, or the missing tubes. Each parallel pass in the evap same will have 'roughly' the same dP, since the system splits & meets again. Practically though, the end manifolds will really determine the true velocity distribution across each circuit. Also probably have to factor in the 2x length of the 7c versus the 14c - haven't gone through the hand calcs fully. You could plot the data I provided with circuits on horizontal axis & dP on vertical axis. Then curve-fit & estimate from there...Last edited by desA; 31-12-2010 at 02:52 PM.
31-12-2010, 07:15 PM #26
31-12-2010, 10:30 PM #27
What is the heat source for the evap?
01-01-2011, 11:37 AM #28
01-01-2011, 06:17 AM #29
Single circuit. 1c. dP/L=8.77 kPa/m ; dP=1896 kPa = 18.96 bar
7c. 2 unlinked tubes. dP/L=0.248 kPa/m ; dP=7.66 kPa = 0.0766 bar
14c. 2 unlinked tubes. dP/L=0.0696 kPa/m ; dP=1.07 kPa = 0.0107 bar
The useful feature here is to compare the dP/L values i.e. the pressure loss per meter of pipe run, in either the 1c, 7c, or 14c configurations.
dP = (dP/L)*L ; where L=pipe length.Engineering Specialist - Cuprobraze, Nocolok, CD Technology
01-01-2011, 09:26 AM #30
- Sep 2007
- Split Croatia
- 57
- 6,151
- 6
- 36
Some good software:
http://www.nist.gov/el/building_envi...d_software.cfm
I think it wont tell you speed, but it will tell you pressure drop.
01-01-2011, 09:01 PM #31
Your load is not steady state, so massive differences in working pressures occur, I now understand the need to know your velocity through out the evap, I am not sure what velocities you require to ensure that oil logging/filming is limited (when you are changing phase), maybe some others have this required data
02-01-2011, 04:30 AM #32
The info I quoted comes from a commercial evap coil design program. Their pressure drops seem credible.
02-01-2011, 09:24 AM #33
02-01-2011, 09:41 AM #34
With R410a the pressure drop on either case is pretty minimal, less than 1C on your sst, I would be more worried about oil logging, at these lower velocities and pipe volume (will the compressor run out of oil over time)
02-01-2011, 09:53 AM #35
Well, for the moment, these systems are running on R407c but we want to change this to R410a. We then can install smaller copper, 3/8" will then be our choice.
But the R407c is a special case, especially if you should encounter a pressure drop of around 1 bar along the line . You then should measure the same temperature (not same pressure) at the end and beginning of the copper.
My colleague is now measuring only at the outlet and he's measuring 4.5 bar ( equals 0°C ) and he's thinking that this is the same all over the line, from beginning till the end.
I know think he's right and I'm wrong. I thought he should face much larger DP's over 70 m copper.
To be 100% sure and to convince myself, I will make a practical setup in my evening classes and connected different lengths of copper to a speed regulated compressor.It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.
02-01-2011, 10:07 AM #36
You will have a bigger tempertaure difference with R407C, approx 2.5C.
+2.5Cevap at inlet and 0C sst at outlet.
02-01-2011, 11:02 AM #37
Testing testing testing testing...
02-01-2011, 11:06 AM #38
Testing testing testing testing - am I being limited to the number of words I can post?
02-01-2011, 11:08 AM #39
Internal Server Error
The server encountered an internal error or misconfiguration and was unable to complete your request.
Please contact the server administrator, dez@clanram.com and inform them of the time the error occurred, and anything you might have done that may have caused the error.
More information about this error may be available in the server error logOnly the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
02-01-2011, 11:09 AM #40
Thus - if you had 1bar pressure drop along a single length (70m + lots of bends) then you would have 0.25Bar pressure drop along two parallel 70m lengths. But then you would also have twice as much pipe surface with two 70m lengths. So you half the lengths each to 35m. Now your pressure drop will be 0.125Bar.
02-01-2011, 11:13 AM #41
Testing testing testing ...
Testing new line
Testing fractions 1/4 and 1/2 and 1/3
Testing brackets ()
Testing editing...
Testing editing again...
Cool, editing worked twiceLast edited by DTLarca; 02-01-2011 at 12:07 PM.
02-01-2011, 10:24 PM #42
For 1/2" pipe add about 0.75 meters for every 180° U-Bend per attached image.
Low speed Variable Speed Screw Chiller
By MelbourneEngg in forum Technical SpeculationsReplies: 4Last Post: 02-07-2010, 02:33 PM -
Setting Daikin VRV indoor unit fan speed
By mchild in forum Air ConditioningReplies: 8Last Post: 24-10-2009, 07:34 AM -
LG heat pump problem
By back2space in forum Heat PumpsReplies: 132Last Post: 01-02-2009, 11:23 PM -
Speed control of the compressor
By Peter_1 in forum Air ConditioningReplies: 10Last Post: 19-12-2007, 07:51 AM -
Thermo King OptiSet
By REEFER-TEK in forum TransportReplies: 4Last Post: 06-12-2007, 07:23 PM