    Hi ive come across some machines that specify that the refrigerant charge gets weighed in. Now the question remains which im just verifying the answer i was given, does it have to be charged in with liquid or vapor?



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Charging by weight

    Ah the old refrigeration conundrum - What weighs more, 1lb of vapour or 1lb of liquid?

    What answer were you given and what's your thinking behind it mate?
    Health and safety first..........unless I'm in a hurry.

  3. #3
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Charging by weight

    Quote Originally Posted by tudorice View Post
    Hi ive come across some machines that specify that the refrigerant charge gets weighed in. Now the question remains which im just verifying the answer i was given, does it have to be charged in with liquid or vapor?

    It depends on the refrigerant, if its a blend then yes it needs to leave the bottle as a liquid.
    It depends on a lot of things such as system size, ambient temperatures, type of refrigerant, if you need to get the whole charge in before running the system, as to which method is best at the time.

    What type of system are you working on?

  4. #4
    Join Date
    Oct 2009
    Location
    Pietermaritzburg
    Age
    41
    Posts
    40
    Rep Power
    0

    Re: Charging by weight

    the systems vary, but mostly R22, R134a and R404a, sometimes R410a. I normally would charge 134a 404a and 410a as liquid, the reason i ask. I recently worked on a scotsman ice machine that spec was 1.5kg of R22. Now i replaced the compressor tecumseh FH5522e originally had AH5522E. but when i charged 1.5kg in it was way overcharged.

  5. #5
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Charging by weight

    R134a and R22 can be charged as either a vapour or liquid as they are single component refrigerants.
    R404A ,and R410A less so, need to leave the bottle as a liquid to ensure the propper blend is maintained.

  6. #6
    Join Date
    Oct 2009
    Location
    Pietermaritzburg
    Age
    41
    Posts
    40
    Rep Power
    0

    Re: Charging by weight

    thought as much, but in the case of the R22 ice maker. 1.5kg of vapor or 1.5kg of liquid? I normally just charge until the superheat is right

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Charging by weight

    1.5Kg is 1.5kg. If its over charged with 1.5KG of liquid it will be overcharged with 1.5KG of vapour too. Its the same volume once its in the system.
    The main thing with liquid charging is that it is easy to slug the compressor, dilute the oil or overcharge the system as the refrigerant is entering the system relatively quickly.

  8. #8
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Charging by weight

    My electronic scales know when it's weighing liquid or vapour and that makes it easy to use as well.
    Lawrie

  9. #9
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Charging by weight

    Quote Originally Posted by tudorice View Post
    thought as much, but in the case of the R22 ice maker. 1.5kg of vapor or 1.5kg of liquid? I normally just charge until the superheat is right
    Tayters got it right .......What is the difference? 1kg of feathers or 1 kg or lead?
    Last edited by nevgee; 31-12-2010 at 12:19 AM.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  10. #10
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Charging by weight

    Quote Originally Posted by lawrence1 View Post
    My electronic scales know when it's weighing liquid or vapour and that makes it easy to use as well.
    Lawrie

    I would be interested in knowing how do they know?
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  11. #11
    Join Date
    Apr 2008
    Location
    UK
    Posts
    215
    Rep Power
    17

    Re: Charging by weight

    I may get shot down in flames here, but as a general rule charge any refrigerant that begins with a no.4 only in it's liquid phase...

  12. #12
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Charging by weight

    Quote Originally Posted by monkey spanners View Post
    1.5Kg is 1.5kg. If
    Its the same volume once its in the system.

    .

    I'm sure you meant mass
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  13. #13
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Charging by weight

    everyone hold up their hands that don't charge with liquid .... be truthfull now
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  14. #14
    Join Date
    Feb 2009
    Location
    Australia
    Posts
    272
    Rep Power
    16

    Re: Charging by weight

    nevgee,
    when i place an empty cylinder on my scales it reads that weight,,,,when i place a full cylinder on my scales it reads that weight too.

  15. #15
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Charging by weight

    Quote Originally Posted by lawrence1 View Post
    My electronic scales know when it's weighing liquid or vapour and that makes it easy to use as well.
    Lawrie
    Ok? ...... you say your scales know the difference between vapour and liquid? I was curious how they did this?
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  16. #16
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Charging by weight

    Quote Originally Posted by Gingerair View Post
    I may get shot down in flames here, but as a general rule charge any refrigerant that begins with a no.4 only in it's liquid phase...
    R400 gases are zeotropes and as Monkey says they need to be charged as a liquid (unless I suppose you are going to use the whole bottle up).
    R500 are azeotropes which can (along with the other remaining refrigerants) be charged as vapour or liquid.

    If not, I'm next to you in the firing line.

    Happy New Year!

    Andy.
    Health and safety first..........unless I'm in a hurry.

  17. #17
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: Charging by weight

    Quote Originally Posted by nevgee View Post
    I'm sure you meant mass
    I'd like to think thats what i meant too



    I have an idea that, though we weigh in refrigerant, what the system 'sees' is volume, so we might put a kilo of R22 but only need 600 grams of R290 to do the same work, what the system needs is a litre of liquid.

    Jon

  18. #18
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Charging by weight

    Quote Originally Posted by tudorice View Post
    the systems vary, but mostly R22, R134a and R404a, sometimes R410a. I normally would charge 134a 404a and 410a as liquid, the reason i ask. I recently worked on a scotsman ice machine that spec was 1.5kg of R22. Now i replaced the compressor tecumseh FH5522e originally had AH5522E. but when i charged 1.5kg in it was way overcharged.
    Assuming the rest of the system was functioning correctly and the compressor was the correct replacement then I'd have charged by the data plate as well. I've been caught out though taking the plate as gospel I now make sure the charge is correct by measurements afterwards. This particular unit had head pressure through the roof, I recovered roughly twice as much as the data plate, discovered the defrost heater wired permanently on, recharged to the specified weight after rewiring controller. Went back the next day with my tail between my legs to find the system short of charge. Only then did it click that the charge was right all along
    Still, got another free lunch out of it!

    Cheers,

    Andy.
    Health and safety first..........unless I'm in a hurry.

  19. #19
    Join Date
    Oct 2009
    Location
    Pietermaritzburg
    Age
    41
    Posts
    40
    Rep Power
    0

    Re: Charging by weight

    thats what i thought monkey spanners. Bloody so - called senior technicians poking holes in my brains. He claimed that i must only charge with liquid no matter the refrigerant, that if i charge with vapor that not enough liquid will be in the system. LOL

  20. #20
    Join Date
    Dec 2007
    Location
    lebanon
    Posts
    130
    Rep Power
    17

    Re: Charging by weight

    hi
    you mention that you have replaced the compressor&refrigerant r 404 has different structure and it has different molecule so that is the reason of over charged scotsman ice machine you can charge it by throttle way thats mean thru suction open and close suction must be at 55 psi at the begenning of the refrigeration cycle&32 psi at harvest

Similar Threads

  1. Liquid charging through the suction side
    By deu58 in forum Fundamentals
    Replies: 13
    Last Post: 02-07-2010, 05:23 AM
  2. Why is suction gauge reading retard during charging?
    By acrefconsultant in forum Technical Discussions
    Replies: 10
    Last Post: 27-09-2009, 08:57 PM
  3. Frequent refrigerant charging
    By desaipt2003 in forum Trouble Shooting
    Replies: 16
    Last Post: 31-03-2009, 02:37 AM
  4. HELP with charging
    By damo1206 in forum Refrigerants
    Replies: 4
    Last Post: 27-11-2008, 12:37 AM
  5. 18 seer AS charging problem,best way?
    By nagzul in forum Air Conditioning
    Replies: 3
    Last Post: 01-05-2008, 07:44 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •