    Receiver starving for liquid



    I had a possible problem with liquid stacking up and not returning to the receiver. Unfortunately my compressors are liquid injection cooled and the compressors shut down on high oil temps. Does anyone out their no some possible diagnostics to prove if the liquid is actually stacking up and if so what are some solutions to help get it to return? Thank you all for any input you may be able to provide.I'm scratching my head on this one?



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Receiver starving for liquid

    Too cold outside.

  3. #3
    Join Date
    Jun 2009
    Location
    Canada
    Age
    55
    Posts
    82
    Rep Power
    15

    Re: Receiver starving for liquid

    I agree with Magoo, liquid is most likely in condenser or condensers. Problem is probably worse during low load conditions. I've had to shut off condenser circuits or isolate whole condensers in order to drive the head pressure back up to get the liquid back. You can also run the condensers dry if the are evaporative.

  4. #4
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Receiver starving for liquid

    Are there multiple condensers? Is there a vent line from the receiver to the condenser inlet?
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  5. #5
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Receiver starving for liquid

    Rcsac,

    Can you please send us a simple drawing of the connections condensers «» receiver?

    Any way, that could be caused by:

    - Lack of NH3;
    - Connections between multiple condensers and liquid receiver not done correctly.

    Do you have one or more condensers?

    Where do you have the equalizing line between the condenser(s) and receiver?

    Is your system flooded? Does the electrovalve that feed the separator is sealing well?
    To make progress is never good enough, I want to do better and better and better

  6. #6
    Join Date
    Sep 2008
    Location
    United States
    Age
    59
    Posts
    57
    Rep Power
    16

    Re: Receiver starving for liquid

    If you can not valve off a condenser to increase your head pressure (if it is lower than normal) you may be low on charge due to service loss during the past year(i.e. oil bleeding,valve repairs or minor leaks.

  7. #7
    Join Date
    Sep 2010
    Location
    United States
    Posts
    32
    Rep Power
    0

    Re: Receiver starving for liquid

    Check your units for ice build up and fans for proper operation. Or, you could have liquid valves leaking by on the liquid supply lines. If your fans are off and your liquid valves are leaking by then the unit will fill up with liquid and store your ammonia not letting it make it back to be reused. It's helpful to check your receiver site glass levels daily, so you can predict or catch a problem and start looking for an answer sooner than later.

  8. #8
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    48
    Posts
    184
    Rep Power
    20

    Re: Receiver starving for liquid

    Hi,

    If you can answer Sandro Baptista's questions you will get much better relevant answers to help you. However if its asmaller unit you can make use a head pressure cylcling switch. Make sure that you have the correct charge and load on your system. www.isentropictemptech.com

  9. #9
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Receiver starving for liquid

    If you have a gas balance between receiver and hot gas to the condenser, close it and drive liquid out, if water/ evaporative condensers drain water and isolate spray pumps. Then control fan operation, natural convection will do the job.
    magoo

  10. #10
    Join Date
    Dec 2010
    Location
    Oklahoma
    Age
    57
    Posts
    8
    Rep Power
    0

    Re: Receiver starving for liquid

    Thanks for everybody's response, my head pressure was 155# at the time of this issue, the ambient was 57 F with a 82% humidity. We did have an unusually low load condition due to the fact that some of our spiral freezers were down, 33% to be exact. So that is definitely worth looking into. Thank you so much for pointing me in the right direction and everyone have a safe and Happy New Year.

  11. #11
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: Receiver starving for liquid

    Low load would curtainly compound your problem.
    magoo

  12. #12
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Receiver starving for liquid

    Quote Originally Posted by Rcsac View Post
    Thanks for everybody's response, my head pressure was 155# at the time of this issue, the ambient was 57 F with a 82% humidity. We did have an unusually low load condition due to the fact that some of our spiral freezers were down, 33% to be exact. So that is definitely worth looking into. Thank you so much for pointing me in the right direction and everyone have a safe and Happy New Year.
    57 F isn't cold. Most likely spiral liquid solenoids are leaking and liquid is in idle evaporators.

  13. #13
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Receiver starving for liquid

    I've had non-condensibles holding liquid NH3 up in an evaporative condenser before.

    Is this a new problem with the plant?

  14. #14
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Receiver starving for liquid

    Quote Originally Posted by DTLarca View Post
    Are there multiple condensers? Is there a vent line from the receiver to the condenser inlet?
    Just an image for reference...
    Attached Images Attached Images
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  15. #15
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Receiver starving for liquid

    Quote Originally Posted by Superfridge View Post
    I've had non-condensibles holding liquid NH3 up in an evaporative condenser before.

    Is this a new problem with the plant?
    This can happen if evaporative condensers have wrong piping or air purger doesn't work properly.

  16. #16
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Receiver starving for liquid

    Quote Originally Posted by Superfridge View Post
    I've had non-condensibles holding liquid NH3 up in an evaporative condenser before.

    Is this a new problem with the plant?

    Despite the increase of the total pressure due to the non condensables gases partial pressure effect I can't see how this effect will influence the Rcsac main problem.
    To make progress is never good enough, I want to do better and better and better

  17. #17
    Join Date
    May 2009
    Location
    New Zealand
    Posts
    141
    Rep Power
    15

    Re: Receiver starving for liquid

    Quote Originally Posted by Sandro Baptista View Post
    Despite the increase of the total pressure due to the non condensables gases partial pressure effect I can't see how this effect will influence the Rcsac main problem.
    I have experienced purging non-condensibles to find an increased receiver level afterwards. I assumed the N/C's trapped above the tower drain leg U traps restricted liquid draining freely from the tower bundle.

    Could be wrong.......have been before.

  18. #18
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Receiver starving for liquid

    Rsac, would be kind/polite if you came back what happened so far. We helped you - I think - help us now also what you found.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  19. #19
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Receiver starving for liquid

    Quote Originally Posted by Superfridge View Post
    I have experienced purging non-condensibles to find an increased receiver level afterwards. I assumed the N/C's trapped above the tower drain leg U traps restricted liquid draining freely from the tower bundle.

    Could be wrong.......have been before.
    Yah, probably you're right!
    To make progress is never good enough, I want to do better and better and better

  20. #20
    Join Date
    Dec 2010
    Location
    Oklahoma
    Age
    57
    Posts
    8
    Rep Power
    0

    Re: Receiver starving for liquid

    Sorry for the delayed response guys. After gathering all the data there were a couple of factors that came in to play on this one, non condensibles was not one of them, i beleive if it was we would have seen an increase on our purger count. However, we had difficulties maintaining our temps on the prod. floor in the summer monthes because there were some unconditioned spaces that were seperated by strip curtains. The proper fix would have been to condition them, but with our tight budget we installed automated doors. Worked out great, floor temps/freezer temps but. Here comes cooler temps, low ambients with higher than usual humidity and our wonderful doors hold back the heat load that we our used to expiriancing, the liquid stacks in the piping on the roof. Thats a lot of volume you can fill. On top of that production had a line interuption and was forced to shut down, what did they do, they shut the fans off only to the spiral freezer but do not take the refrigeration controls out of refrigeration mode, great, now weve stored a considerable more amount of liquid and with an undersized receiver she ran out. Did I mention undersized, yes weve added evaporators, recirculators, condensers, oops. So the fix. Create production interupt procedures for the spiral freezers, increase the volume of the receiver, and start shutting off liquid to the production floor evaporaters. But my mind is not closed nor my ego too big. Does anyone else have some suggestions.

  21. #21
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Receiver starving for liquid

    Sorry Rcsac,

    Can you organize better/individualize the several subjects you have mentioned as well as your question?
    To make progress is never good enough, I want to do better and better and better

  22. #22
    Join Date
    Dec 2010
    Location
    Oklahoma
    Age
    57
    Posts
    8
    Rep Power
    0

    Re: Receiver starving for liquid

    Yes, I will have to get back to you on that one.
    ????????????????????????????????????????

  23. #23
    Join Date
    Dec 2010
    Location
    Oklahoma
    Age
    57
    Posts
    8
    Rep Power
    0

    Smile Re: Receiver starving for liquid

    I apologize Sandro, we must be struggling with some language barrier issues. Let me ask again.

    1. Are there ways to tell that liquid Nh3 is stacking prior to allowing a receiver vessel to go empty?

    2. What are some fixes to minimize stacking?

    When I use the word STACKING I am meaning Nh3 holding up, flow slowed/stopped, a decrease in pressure
    Differential, not flowing properly.

    I hope this helps you sincerely.

  24. #24
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: Receiver starving for liquid

    Liqiud holding up in condensers ,sometimes liquid drains are stone cold .
    In your climate this could be the case anyway.
    If you have a balance line between main discharge line & top of liquid reciever as well as "P" traps on each it should'nt be to bad.
    You could try carefully opening purge valve on liquid drain from each condenser to see if liqid(if you have a valve there).
    You could try turning plant off to see if reciever level changes, as well as isolate balance line & purge aggresively off top of reciever (maybe hose & run to low side accumulator or similar).

  25. #25
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,020
    Rep Power
    19

    Re: Receiver starving for liquid

    Rcsac,

    RANGER1 has given you good information. I advice to follow his advices
    To make progress is never good enough, I want to do better and better and better

  26. #26
    Join Date
    Mar 2005
    Location
    USA
    Age
    76
    Posts
    638
    Rep Power
    20

    Re: Receiver starving for liquid

    RCSAC, if you are having issues with the plant design due to add-ons and such, it would really benifit you to hire a good refrigeration consultant to do a survey on the plant and see where the problems lie and what it willtake to fix them. I know a very good and experienced consultant (P.E.) in Houston thatprovide the diagonsitic service.

    Ken

Similar Threads

  1. "Unstable" Rack Receiver Liquid Level
    By chweber in forum Commercial
    Replies: 3
    Last Post: 09-02-2009, 08:58 AM
  2. where do you buy a new NH3 receiver?
    By Oregon Jim in forum NH3
    Replies: 12
    Last Post: 24-01-2009, 01:25 AM
  3. Receiver! Needed or not
    By The MG Pony in forum Fundamentals
    Replies: 4
    Last Post: 22-08-2007, 08:51 PM
  4. liquid receiver low level alarm
    By racknovice in forum Supermarket Refrigeration
    Replies: 8
    Last Post: 18-08-2007, 06:53 PM
  5. Starting a compressor, and receiver questions.
    By DaBit in forum Technical Speculations
    Replies: 9
    Last Post: 24-08-2002, 12:37 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •