30-12-2010, 05:05 AM #1
Adding oil to a york chiller compressor
I am a new kid on the block, first time to a chiller
Any one please help to show me how to add the oil to a compressor for York chiller and what tool is need for adding oil. Many Thanks for help
30-12-2010, 06:34 AM #2
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Adding oil to a york chiller compressor
If you have rota-lock valves, you need to bypass system low pressure alarm, connect your manifold gauges, close suction valve until suction pressure is slightly above 0 bar gauge and put charging hose in oil can. When hose is vented of air, close more suction valve to lower pressure below 0 bar and oil will be sucked from can in to compressor crankcase. Take care that hose is always submerged in oil to avoid sucking of air. When oil is enough close manifold and open slowly suction rota-lock to full open to avoid oil hammering.
Take care to not overheat compressor by doing this for extended period of time..Last edited by nike123; 30-12-2010 at 06:38 AM.
30-12-2010, 11:52 AM #3
on some comps there is a valve on the sump under the oil pump if ther is then you can pump oil into the comp its a 3/8 valve so you may need a reducer 3/8 f 1/4 m
30-12-2010, 08:04 PM #4
Or you can use a manual oil pump to push it in via the low pressure side.
Example here...
http://www.wilhelmsen.com/services/m...es/597534.aspxBrian - Newton Abbot, Devon, UK
31-12-2010, 02:54 AM #5
Many Thanks to all the gentlemen for your help. HAPPY NEW YEAR 2011
HelpNeed York chiller literature!
By matrix1004 in forum IndustrialReplies: 8Last Post: 09-12-2010, 09:36 PM -
York YS chiller water connections left vs right hand config
By Pete S in forum CommercialReplies: 1Last Post: 17-06-2010, 06:54 PM -
York Chiller Fault
By kifayat in forum Trouble ShootingReplies: 8Last Post: 11-07-2009, 02:55 PM -
York chiller problems
By robert ames 195 in forum Trouble ShootingReplies: 1Last Post: 12-05-2009, 09:59 PM -
York process chiller repairs
By Matt in forum CommercialReplies: 5Last Post: 23-03-2004, 11:07 PM