    Exclamation walk-in cold room.



    HI guys,
    I have been on this cold room(frezer -20),which somehow a cowboy have replaced a semi hermetic with a scroll ! Besides this,had to rewire all from new as can imagine what ! Now I need to ask about the way the compressor shall stop after a thermostat signal.At present is turning off the contactor for the compressor and condenser fan.I am in the idea of installing a high and low pressure switches as there is not at present ,and the thermostat turn off the liquid line solenoid,to take a pump down,and trip on low pressure.I am afraid that the oil will not be returned back on a normal cycling.Is it effective to try to collect oil back with refrigerant this way.Does the scroll equalise the same as the reciprocating ? My concern was since there was Not installed a suction accumulator.I don't think that this compressor will last for long !! Any ideas ?



  2. #2
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: walk-in cold room.

    fit pressure switches and wire system to pump down and stop on low pressure switch

  3. #3
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: walk-in cold room.

    Martinw58,
    Will it be successful to collect oil from evaporator,because I am afraid that during time will practically force gradually oil out,ending with no oil in compr.Since it's a scroll does it affect from the suction side ?

  4. #4
    Join Date
    Jun 2008
    Location
    NZ
    Posts
    102
    Rep Power
    17

    Re: walk-in cold room.

    So long as velocity in the pipe is correct, (Does the displacement of the scroll match that of the semi?) oil return shouldn't be a problem.

    Does the system have an oil sep fitted?

    Additionally, be careful with your LP cut out setting, as extended operation of a scroll at low mass flow is a recipe for disaster. Better to leave the LP as high as you possibly can without it cycling.

    No HP/LP?

  5. #5
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: walk-in cold room.

    Flyinkiwi,
    Unfortunately as I said,there was someone that replaced the semi hermetic compressor with this scroll!Have no acess to the original compressor,so cannot state that it is adequate for it's capacity.There is no oil separator in system.With regards to the low pressure switch,shall I set to 1/2 Bar.System runs on R22!

  6. #6
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: walk-in cold room.

    Hi,

    Martinw58 has sugested a good way of controling this unit. Remember that when your thermostat energizes the liquid line solenid valve agin when there is need for cooling you release high pressure gas into the evaporator which should push most of the oil back to the compressor. However should you have your fears it is not bad practice to install an oil seperator just to give yourself comfort.

  7. #7
    Join Date
    Aug 2006
    Location
    england
    Age
    50
    Posts
    3,856
    Rep Power
    46

    Re: walk-in cold room.

    Hi Kerrcell,

    If the scroll is sized right for the duty and application then it should be ok. I have had to fit different make and/or models when the correct compressor has been out of stock and the system needs to be running as soon as possible.

    Fit a crank case heater if none is fitted now. If you run it on pumpdown, as Flyinkiwi says, set the lp to as high a cut out as practical, and a wide differential too to prevent short cycling. Or you could just shut the solenoid when the compressor is off, this will help stop liquid migration when the comp is off, especially if the solenoid is near the txv.

    Jon

  8. #8
    Join Date
    Feb 2005
    Location
    sliema
    Age
    52
    Posts
    138
    Rep Power
    20

    Re: walk-in cold room.

    HI Monkey spanners,
    I shall fit a crancase heater around comp.There isn't actually.I think will stick also to feed thermostat output to control solenoid of liquid line,then to trip system on low pressure switch.The solenoid is around 3 mtrs from exp.valve.

Similar Threads

  1. How to prevent the germs living in fresh-cut cold room.
    By monoblocker in forum New Technologies
    Replies: 9
    Last Post: 10-12-2010, 02:43 AM
  2. Blind Cold room specs help
    By frostedflake in forum Trouble Shooting
    Replies: 5
    Last Post: 13-03-2009, 01:49 AM
  3. Installation of cold room
    By Josip in forum Legal-Business-Marketing
    Replies: 12
    Last Post: 12-03-2006, 09:20 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •