    Compressor for island case



    Hello experts,
    I need make island case with built-in condensig unit and capillary tube.
    The air temperature inside may vary from minus 6 C to plus 6 C.
    Should I use LBP or MBP Embraco compressor for condensig unit ?
    Which must be evaporation temperature?

    Thanks for any advice



  2. #2
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Compressor for island case

    Tralex , i didn't understand what you want to build . . . please explain
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  3. #3
    Join Date
    Jul 2005
    Location
    Belarus
    Age
    51
    Posts
    25
    Rep Power
    0

    Re: Compressor for island case

    Hello botrous,
    I'm sorry for my inefficiency to explain what I want.
    Now I drew my question.
    Thank you
    Attached Images Attached Images

  4. #4
    Join Date
    Apr 2001
    Location
    UK
    Posts
    2,099
    Rep Power
    27

    Re: Compressor for island case

    You need MBP or LBP assuming you want to evaporate around -16C
    to achieve -6C

    You need to check Embraco table for that compressor to see if it can achieve the required duty at that evap temp

  5. #5
    Join Date
    Dec 2004
    Location
    LEBANON
    Age
    44
    Posts
    854
    Rep Power
    21

    Re: Compressor for island case

    I agree with Ayub . . . send an email to the Embarco and they can help you select the right compressor for your application or see the Embarco tables
    Engineering, sciences, math, physics and my brain will generate "not responding " soon

  6. #6
    Join Date
    Aug 2005
    Location
    South Africa
    Age
    55
    Posts
    19
    Rep Power
    0

    Re: Compressor for island case

    You also need to check the condenser size if you intend using the existing one. The safest would be to use a standard condensing unit sized to the (new) capacity of the existing evap. Remember the evap will give slighlty more capacity at the high temperature (depending on the delta T of course).