Thread: Rack very acidic
-
27-12-2010, 07:00 AM #1
Rack very acidic
Anyone got an Idea how to remove acid from a rack thats got 5 bitzer 6G's? Whats the best solution...
-
27-12-2010, 11:45 AM #2
Re: Rack very acidic
Hi Ulster man.
The normal thing to do on any system, is to recover the contaminated refrigerant.
Drain and change the oil. Pull a deep vac.
Recharge with fresh refrigerant having fitted burn out liquid line driers.
If the contamination is severe then fitting a suction line filter may well be advisable.
Once the system is runnable then you still may well have to do several filter changes.
A second oil change may also be necessary.
Monitoring the acid levels will decide how many changes are required.
Are the acid levels due to a motor burn out or excessive air/moisture in the system?
-
27-12-2010, 01:33 PM #3
Re: Rack very acidic
Yes, several racks with many burnt out motors, lack of using vac pumps to boot... This is asian markets, washing out compressors with DIESEL i might add too! Got to start somewhere, recovering the refrigerant is the idea thing but money saving is the only answer here... Ill be changing the oil filters etc... are there any products on the market like acid away that comes by the gallon????
-
27-12-2010, 04:17 PM #4
Re: Rack very acidic
fit specific core driers for acid in both suction and liquid, change the oil as often as budget allows, change acid driers every few hours until an improvement is seen, you may still lose compressors in the mean time though!
al
-
27-12-2010, 06:22 PM #5
-
29-06-2011, 05:38 PM #6
Re: Rack very acidic
Moderators....... I cannot start new threads... Whats the problem???
-
29-06-2011, 06:44 PM #7
Re: Rack very acidic
Good advice from Grizzly here.
I have seen some good results from Installing these Oil Separators & Filters on the systems.
http://www.temprite.com/product.asp?...ltkit&aux=true
-
29-06-2011, 09:54 PM #8
Re: Rack very acidic
ulster man how did u manage to find yourself working out there if you dont mind me asking?
-
30-06-2011, 07:05 AM #9
Re: Rack very acidic
Hi Grizzly,
That was on the old days. Today, you can recycle the contaminated gas, use it to flush the acids out out the system, and re-use the recycled gas with total warranty. This is the best way to eliminate all acids from a plant, and an economic one, as you reuse the existing gas. No need to buy fresh refrigerant.
This is the way professionals solve the acids problem.
Regards,
Nando.
-
01-07-2011, 02:25 PM #10
Re: Rack very acidic
What exactly your meaning???
I'll reply by saying that the local labour here are untrained, self taught and thier knowledge of whats going on with the system is very limited.
Im here training them, helping with new designs overseeing instalations as they dont know how to pipe a system properly.
They have local made Bitzer compressor racks with oil controls designed wrong, each compressor running subcoolers and each have own oil seperators piped to resevoir with the bleed valved piped to the suction header on a 2 stage compressor. LOL
So you can guess we are having lots of trouble!!
PS... not far from Thailand either
-
01-07-2011, 02:37 PM #11
Re: Rack very acidic
Yea, I manage to purchase several burn out drier cores both for suction and liquid filters, changed these several times while checking the compressor oil with Lab results and things are getting better. No gas was reclaimed or recycled.
Acid caused by too many burnt out coils that have been rewound using china made copper!
-
03-07-2011, 02:05 PM #12
Re: Rack very acidic
buddy
Similar Threads
-
Rack cannot reach low or medium setpoints
By Hotdoggy in forum Trouble ShootingReplies: 2Last Post: 28-06-2010, 10:51 PM -
opr valve operation in rack system
By coldkeeper1 in forum Supermarket RefrigerationReplies: 2Last Post: 10-12-2009, 06:17 PM -
Electric Load for Refrigeration Rack System
By seanK in forum Supermarket RefrigerationReplies: 6Last Post: 27-06-2009, 02:08 PM -
"Unstable" Rack Receiver Liquid Level
By chweber in forum CommercialReplies: 3Last Post: 09-02-2009, 08:58 AM -
R744 Supermarket Rack
By 750 Valve in forum Supermarket RefrigerationReplies: 5Last Post: 28-07-2006, 03:32 AM