    If I have a Split Air Conditioners with the following Data:
    Cooling Capacity: 18,000 Btu/hr (5.2755 kW)
    Power Input: 2.17 kW

    Some people will calculate EER as follows:
    Option 1:
    Cooling Capcity (Btu/hr) / Power Input (Watts)
    = 18,000/2170 = 8.295

    Option 2:
    Cooling Capacity (kW) / Power Input (kW)
    = 5.2755 / 2.170 = 2.43

    So which one is the correct calculation and what is the difference between both?



  2. #2
    Join Date
    Apr 2008
    Location
    Southampton, England
    Age
    49
    Posts
    1,023
    Rep Power
    36

    Re: Eer

    I'd say option 1 gives you EER.
    Option 2 gives CoP.

    Cheers,

    Andy.
    Health and safety first..........unless I'm in a hurry.

  3. #3
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: Eer

    1 is only valid for countries with IP system.
    Both EER and COP should be W/W or kW/kW.
    EER is summer efficiency.
    COP is winter efficiency.