    cutan Guest

    Unhappy too big condenser??



    hi, i am newbi and i have one question. What happens if you
    put too big water condenser unit on air to water heat pump. Heat pump with cap. tube or tev.
    thanks for anwsers.



  2. #2
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: too big condenser??

    Nothing special if you control your flow of water.

  3. #3
    Join Date
    Nov 2010
    Location
    Germany
    Age
    39
    Posts
    120
    Rep Power
    14

    Re: too big condenser??

    The outlet temperature will depend of water flow.The maximum water temperature at the condenser outlet must not be higher than values reported on operating limits of heat pump producer. In the event of higher temperatures the safety devices will trip causing the unit to shut down. If you can avoid triggering the safety devices, than nothing important will happen.
    Be careful about reading health books. You may die of a misprint.

  4. #4
    cutan's Avatar
    cutan Guest

    Re: too big condenser??

    thanks for the quick response.
    if i understand correctly, if i add some
    more coolant R407c (biger condenser) the system will operate normally. Thanks again.

  5. #5
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: too big condenser??

    Quote Originally Posted by cutan View Post
    thanks for the quick response.
    if i understand correctly, if i add some
    more coolant R407c (biger condenser) the system will operate normally. Thanks again.
    You are not understanding this correctly.
    Refrigerant should be charged by subcooling (for R407C is usually 7K-9K or even more if piping pressure drop is high) at condenser outlet WHEN unit is near set-point and condensation saturation temperature is at design temperature (usually at 40°C).
    You cannot add SOME amount. It need to be as described.

  6. #6
    cutan's Avatar
    cutan Guest

    Re: too big condenser??

    thanks.
    i did mean by superheat, i just wrote this in simple maner.

  7. #7
    cutan's Avatar
    cutan Guest

    Re: too big condenser??

    subculing

  8. #8
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: too big condenser??

    Quote Originally Posted by cutan View Post
    subculing
    subcooling

Similar Threads

  1. Replies: 24
    Last Post: 19-08-2010, 10:50 PM
  2. Replies: 2
    Last Post: 08-06-2010, 11:12 PM
  3. How to measure COP (evaporative condenser)
    By Juho in forum Technical Discussions
    Replies: 5
    Last Post: 04-06-2010, 07:08 PM
  4. Evaporative Condenser system COP
    By Juho in forum Commercial
    Replies: 0
    Last Post: 03-06-2010, 09:23 AM
  5. Air Cooled Condenser Leakage Problem with R-404A
    By RADHAKRISHNARAO in forum Technical Discussions
    Replies: 19
    Last Post: 30-07-2008, 12:21 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •