    Carrier technicians please help!



    Carrier 30GX chiller
    Guys i got this chiller, and for some reason it is running in "overide". I looked on the connection therminal no 73 and 74 and it is not connected. I also looked at inputs menu 2 (no4) and it shows it is in the open position. And in setpoints menu(2) no5 it is set at 100%. Any ideas what i am missing?



  2. #2
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier technicians please help!

    Override covers a multitude of conditions such as low saturated suction temps, high discharge pressures low discharge superheat etc .
    Basically the chiller circuit concerned won't allow any extra capacity to load up and in some cases will unload capacity so maybe if you gave us a log of what the chiller is doing we might be able to help.
    exv position
    sat suction temp
    discharge pressure
    discharge superheat
    water in
    water out
    circuit capacity
    total capacity

    What is the chiller doing that makes you think their is a problem.

  3. #3
    Join Date
    Dec 2010
    Location
    South Africa
    Age
    48
    Posts
    5
    Rep Power
    0

    Re: Carrier technicians please help!

    I wil have a look at al that and give you some feedback. The return water goes up to 17deg c. but comp.(a) does not start. If i put comp(b) in a alarm, then comp(a) start up. Then i reset the alarm comp(b) and the chiller runs good until it cycle on temp. The leaving water goes down to 5deg c Then the problem just repeat itself. The chiller does not give an alarm, it just runs on a overide(limit) whitch cause the unit not to run at full cappasity

  4. #4
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier technicians please help!

    So if A circuit runs ok when B circuit is forced into alarm, have you tried putting A circuit into alarm and see if B circuit loads up.
    Let the water temp get high so their is plenty of load then start to log the chiller. With your log you will get a idea whats happening.
    Forgot to mention check the motor temp as well when you do your log.
    I forgot to ask if you have a controls manual.

  5. #5
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Carrier technicians please help!

    if the chw load is not constant the unit will not load up 100% as the unit see's the temp dropping quickly and ticks over

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier Chillers
    By Ed Burris in forum Technical Discussions
    Replies: 6
    Last Post: 27-03-2010, 02:00 AM
  3. Carrier 42XPF100 spares availability
    By rob_h1978 in forum Air Conditioning
    Replies: 0
    Last Post: 11-02-2010, 11:08 AM
  4. Geoff in NY ~ Carrier Parts
    By Futsal1st in forum Trouble Shooting
    Replies: 6
    Last Post: 30-12-2009, 04:07 AM
  5. Help identifying carrier HiWall dom. split
    By paul_h in forum Air Conditioning
    Replies: 4
    Last Post: 12-12-2008, 09:12 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •