    Good Morning and Merry Christmas!! I hope this is the right forum for help with an answer for my problem.
    I have a Frigidaire upright freezer model # PLFU1778ES4.
    I have checked the defrost timer and it is working.

    My problem is that I have to keep the Cold Control set at about 1/2 on the dial to maintain 0 degrees. It will then start short cycling of about 40 seconds on and 40 seconds off. I put a new cold control in yesterday and the dial still has to be set at about 1/2 on a dial that goes up to 7. I set it on 2 and it ran all night and this morning it was -10 below zero. I have tried to reset and control it today several times, and it seems no matter how low I set it, it will start. Please give me some ideas of what to look at now. Thanks Terry



  2. #2
    Join Date
    Oct 2008
    Location
    mallorca, spain,
    Age
    75
    Posts
    768
    Rep Power
    19

    Re: Cold Control not working

    hi terry,
    you say you fitted a new cold control? is that a new thermostat?

  3. #3
    Arizona Terry's Avatar
    Arizona Terry Guest

    Re: Cold Control not working

    Good Morning, Yes it is the T-stat that controls the compressor. Thanks

  4. #4
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: Cold Control not working

    Hi

    Merry christmas to you. I am not familiar with the exact model you mensioned here. However I am more than confidant I can help you out with ideas if you tell me which type of thermostat between digital and analogue you are dealing with.

  5. #5
    Arizona Terry's Avatar
    Arizona Terry Guest

    Re: Cold Control not working

    Hello Press, It is a Analog twist dial on the cold control. I am guessing that is also the thermostat for this freezer. I have it set at about 1/2 on the dial and it is still doing the same thing as it was before I changed the cold control. Thanks

  6. #6
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: Cold Control not working

    Arizona Terry

    Judging from the 40 sec short cycles you mensioned at the begining of the thread do not ignore your thermal over load (clixon) however if nothing is wrong with it, I would like to think that your thermostat is faulty. However before you make any conclusions to this effect I advise you to by-pass the thermostat and check if the unit achieve the desired lowest temperature.

Similar Threads

  1. Humidity Control for fresh fruit cold room
    By mechman in forum Industrial
    Replies: 7
    Last Post: 05-09-2010, 03:26 AM
  2. cold river water
    By eftimios in forum Fundamentals
    Replies: 8
    Last Post: 09-11-2008, 06:37 PM
  3. cold room
    By CHILLED4 in forum Trouble Shooting
    Replies: 5
    Last Post: 16-11-2007, 11:44 PM
  4. expansion valve aint cold
    By justinworne in forum Trouble Shooting
    Replies: 6
    Last Post: 26-07-2006, 10:52 PM
  5. is my fridge working properly?
    By vincec in forum Trouble Shooting
    Replies: 1
    Last Post: 15-01-2002, 09:55 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •