25-12-2010, 11:06 AM #1
Relation on coil temp. and total cooling capacity
Hi guys i have one question why when i make a increasing on coil temp. for example from ( 80/67F dbt/wbt) to 89/69 dbt/wbt
capacity it will increased?
I hope somebody will help me as soon as possible
-
29-12-2010, 07:37 PM #2
Re: Relation on coil temp. and total cooling capacity
Carrier performance tables suggest about 900btu/1000 cfm/(T-80). So at 89 deg entering water temperature, the sensible capacity would increase 8100 btuh for each 1000 cfm of evaporator air flow. Latent capacity is not affected.
Best bet is to contact the manufacturer's rep if you want a more exact answer.
-
30-12-2010, 05:54 PM #3
Re: Relation on coil temp. and total cooling capacity
This manufacturer does a free software for coil selection / engineering queries etc. I haven't used the current version but the older versions used to be quite good for working out performance for new or existing coils.
http://www.spcoils.co.ukReality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]
-
10-01-2011, 07:37 AM #4
Re: Relation on coil temp. and total cooling capacity
thanks guys
I means when i make increase on on coil Temp capacity will increase also
specially when if this change in wbt
Similar Threads
-
Lower Air off temp required
By Collie in forum Air ConditioningReplies: 12Last Post: 22-07-2010, 05:53 PM -
Suction gas <-> liquid line heat exchange and performance gains
By DaBit in forum Technical SpeculationsReplies: 30Last Post: 18-05-2010, 01:52 PM -
Use of R22 compressor in R12 application?
By flintsys in forum CommercialReplies: 45Last Post: 13-04-2010, 07:43 PM -
indoor split ice
By SkyWalker in forum Air ConditioningReplies: 5Last Post: 07-09-2009, 04:51 PM -
total fresh air handler
By Lc_shi in forum FundamentalsReplies: 3Last Post: 19-12-2005, 09:31 AM