    Exclamation Relation on coil temp. and total cooling capacity



    Hi guys i have one question why when i make a increasing on coil temp. for example from ( 80/67F dbt/wbt) to 89/69 dbt/wbt
    capacity it will increased?

    I hope somebody will help me as soon as possible



  2. #2
    Join Date
    Apr 2009
    Location
    Panacea, Florida
    Age
    87
    Posts
    76
    Rep Power
    16

    Re: Relation on coil temp. and total cooling capacity

    Carrier performance tables suggest about 900btu/1000 cfm/(T-80). So at 89 deg entering water temperature, the sensible capacity would increase 8100 btuh for each 1000 cfm of evaporator air flow. Latent capacity is not affected.

    Best bet is to contact the manufacturer's rep if you want a more exact answer.

  3. #3
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: Relation on coil temp. and total cooling capacity

    This manufacturer does a free software for coil selection / engineering queries etc. I haven't used the current version but the older versions used to be quite good for working out performance for new or existing coils.

    http://www.spcoils.co.uk
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  4. #4
    Join Date
    Oct 2009
    Location
    kuwait
    Posts
    9
    Rep Power
    0

    Re: Relation on coil temp. and total cooling capacity

    thanks guys


    I means when i make increase on on coil Temp capacity will increase also
    specially when if this change in wbt

Similar Threads

  1. Lower Air off temp required
    By Collie in forum Air Conditioning
    Replies: 12
    Last Post: 22-07-2010, 05:53 PM
  2. Suction gas <-> liquid line heat exchange and performance gains
    By DaBit in forum Technical Speculations
    Replies: 30
    Last Post: 18-05-2010, 01:52 PM
  3. Use of R22 compressor in R12 application?
    By flintsys in forum Commercial
    Replies: 45
    Last Post: 13-04-2010, 07:43 PM
  4. indoor split ice
    By SkyWalker in forum Air Conditioning
    Replies: 5
    Last Post: 07-09-2009, 04:51 PM
  5. total fresh air handler
    By Lc_shi in forum Fundamentals
    Replies: 3
    Last Post: 19-12-2005, 09:31 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •