    AC Split unit working under 16ºC



    Hi and Merry Christmas to all

    I work for a company in Mozambique that does air conditioning work.

    At 2 diferent sites we are facing the same problem:

    in the server rooms, normal wall split units were installed and the users run them all the time at 16ºC. The sution line, although well insulated with armaflex is always condensating, creating drops on ceiling. We replaced the inslation but it is still doing the same thing.

    Is this a insulation problem of the piping or can be related with the fact that the ac split units are runing at 16ºC?



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: AC Split unit working under 16ºC

    Running the splits at 16c is defiantly not a good idea.I doubt there is anything in the server room that requires such a low ambient to operate,The splits probably never achieve set point and run continuously .And if you have any air breaks in the insulation this will cause the suction pipe to sweat profusely,if ice then starts to form on the evap coil this will only start to compound the problem as the back pressure starts to drop off
    May be an idea to use thicker walled armaflex if the humidity is high
    Try operate the splits a few degrees higher about 20-21c ,if they can maintain temp shouldn't have any issues
    Cheers

    Stu
    Last edited by stufus; 25-12-2010 at 11:41 AM.
    Tool's ? check ! Condom's ? check !
    If you can't fix it , f*ck it !!!

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: AC Split unit working under 16ºC

    As Stufus said, raise the temperature set point.

    Also make sure that the insulation is vapour sealed at all joints and ends; don't not squeeze it with tie-wraps.
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Sep 2007
    Location
    philippines
    Posts
    8
    Rep Power
    0

    Re: AC Split unit working under 16ºC

    Maybe you have a humidity problem inside your server room beacause I have been to many server rooms and temperatures reaches up to 18 below deg C. As far as i know normal splits are for comfort cooling only and are not design for server rooms application instead try using presicion aircon that controls humidity and temperature. And for installation of refrigerant pipes do not install it above your server rooms or water drops pouring on your computers and servers will be your next problems.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: AC Split unit working under 16ºC

    Install outdoor fan speed regulation to stop over condensing and system over performance, and condensation problem.

  6. #6
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: AC Split unit working under 16ºC

    Quote Originally Posted by Magoo View Post
    Install outdoor fan speed regulation to stop over condensing and system over performance, and condensation problem.
    OH MY! Magoo, you used the "O.C" word!!! Remember the thread started back some months ago ?? .. No such thing.. ask Gary. (Pssst! i know what you mean)
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  7. #7
    Join Date
    Jul 2007
    Location
    Australia
    Age
    50
    Posts
    1,845
    Rep Power
    20

    Re: AC Split unit working under 16ºC

    Yes, you mean too low a head pressure

  8. #8
    Join Date
    Apr 2009
    Location
    Panacea, Florida
    Age
    87
    Posts
    76
    Rep Power
    16

    Re: AC Split unit working under 16ºC

    The problem here is the user, and you need to advise them. If you can obtain the specs for one of the servers, you will be able to show them that the units are rated for temperatures up to 40C with a rh range of 20 - 80%. IBM recommends a data center temperature of 22C.
    http://publib.boulder.ibm.com/infoce...ditydesign.htm

    Server rooms are generally not as controlled as data centers, and are usually contiguous with office space, where the dew point could occasionally rise above 16C, causing condensation on server cabinets. So 16C is definitely not a good idea.

    However, the suction line condensation may still occur, even at reasonable space temperatures, so the insulation needs to cover all of the exposed suction-side components, have all of the joints sealed, and be finished with a tight vapor barrier.

  9. #9
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: AC Split unit working under 16ºC

    Along with the other posts, there is also likely chance the systems were sized incorrectly. Their total duty being used without consideration for the sensible load and shr of the indoor units.
    Typical indoor AHU's have only 0.7 shr in which case they could be undersized by 30% and the user sees a low performance, hence turning down the stat to 16C
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  10. #10
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: AC Split unit working under 16ºC

    Hi Mikeref and Paul.
    I will wash my mouth out with salt.
    magoo

  11. #11
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: AC Split unit working under 16ºC

    Quote Originally Posted by nevgee View Post
    Along with the other posts, there is also likely chance the systems were sized incorrectly. Their total duty being used without consideration for the sensible load and shr of the indoor units.
    Typical indoor AHU's have only 0.7 shr in which case they could be undersized by 30% and the user sees a low performance, hence turning down the stat to 16C
    The only stable solution to this is to use a larger indoor unit - not to also use a larger outdoor unit.

    Where do you think the other 30% compressor capacity goes if there happens to be a shortage of moisture in the room?
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  12. #12
    nevgee's Avatar
    nevgee is offline Veteran Poster I am starting to push the Mods: of RE
    Join Date
    May 2006
    Location
    Yorkshire
    Age
    72
    Posts
    417
    Rep Power
    18

    Re: AC Split unit working under 16ºC

    A differrent balance point will be achieved, with a lower suction pressure, and lower duty from the compressor.
    Reality is an elusion created by alcohol deficiency. Quaff and enjoy. [Yorkshire, UK]

  13. #13
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: AC Split unit working under 16ºC

    Quote Originally Posted by nevgee View Post
    Along with the other posts, there is also likely chance the systems were sized incorrectly. Their total duty being used without consideration for the sensible load and shr of the indoor units.
    Typical indoor AHU's have only 0.7 shr in which case they could be undersized by 30% and the user sees a low performance, hence turning down the stat to 16C
    Too true, i've seen a/cs sized for specific applications only to find room layout has changed with extra equipment added or wall removed and another room added. Air-con now cannot cope with demand.
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  14. #14
    Join Date
    Dec 2010
    Location
    Mozambique
    Age
    56
    Posts
    11
    Rep Power
    0

    Re: AC Split unit working under 16ºC

    Thank you very much for your coments.

    We already advise teh user to set the temperature at 20 ºC, it is more than enough, but with no results.

    We have insulated the pipes again and sealed the joints, but it is still droping.

    We will take in consideration your comenmts.

    Thanks again

  15. #15
    Join Date
    Jul 2010
    Location
    NTH.QLD Australia
    Age
    62
    Posts
    1,730
    Rep Power
    32

    Re: AC Split unit working under 16ºC

    This condensation problem, is it moisture forming on the outside of insulation only? Is there condensation in other areas like under the evaporator? Assuming this a/c has refrigerant expansion at condensing unit, then both lines are independantly insulated right?
    To the optimist, the glass is half full. To the pessimist, the glass is half empty.

  16. #16
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: AC Split unit working under 16ºC

    If you still have condensation, then you've used too thin isolation or low quality isolation or gaps.
    If condensation comes on your isolation, then the isolation is faulty, not the split.
    What band and thickness have you used? What thickness of isolation are you using, what brand of isolation, what type of that band. What's your SH and TE
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

Similar Threads

  1. Solar AC split unit
    By sonic in forum New Technologies
    Replies: 6
    Last Post: 21-11-2010, 10:06 PM
  2. Daikin Split inverter external unit fault
    By apounder in forum Trouble Shooting
    Replies: 2
    Last Post: 18-05-2010, 10:47 AM
  3. Split board consumer unit
    By Swipe in forum Air Conditioning
    Replies: 34
    Last Post: 07-05-2009, 07:11 PM
  4. Loud Rining: Indoor Unit or Split AC
    By harry.finn in forum Trouble Shooting
    Replies: 7
    Last Post: 10-11-2008, 09:35 PM
  5. Thermo King OptiSet
    By REEFER-TEK in forum Transport
    Replies: 4
    Last Post: 06-12-2007, 07:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •