    bitzer screw pack help please



    the pack is running a chilled production area and had a heat exchanger fitted we attended site to find a hp line ruptured and also found the heat exchanger passing across to the water side. the water has been shut off for 4 weeks and we noticed the ball valve on the water side had ruptured due to the line freezing with water. we removed the heat exchanger and vacced the system out we then re charged with 500kg of r404 to find the system was full of water and we were not getting the sufficient back pressure. we now need to reclaim the system and get rid of the water there are 6 evaps on this system what would the best way to approach this be as i feel the system is very heavily contaminated.

    thanks for your help in advance guys its much appreciated.



  2. #2
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: bitzer screw pack help please

    Quote Originally Posted by Mr-Frosty View Post
    the pack is running a chilled production area and had a heat exchanger fitted we attended site to find a hp line ruptured and also found the heat exchanger passing across to the water side. the water has been shut off for 4 weeks and we noticed the ball valve on the water side had ruptured due to the line freezing with water. we removed the heat exchanger and vacced the system out we then re charged with 500kg of r404 to find the system was full of water and we were not getting the sufficient back pressure. we now need to reclaim the system and get rid of the water there are 6 evaps on this system what would the best way to approach this be as i feel the system is very heavily contaminated.

    thanks for your help in advance guys its much appreciated.
    Install drain points at all lowest points (each evap etc), removal of free water.
    Get air compressor, cool air resaviour (remove moisture), then Heat the air, then introduce into the system, blowing through the system, leave for a time. Nitrogen and vac.
    change oil, filters dries.
    Time and Heat, more heat less time!

  3. #3
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: bitzer screw pack help please

    Interested to know how if the system was full of water you managed to evacuate the system without noticing?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  4. #4
    Join Date
    Oct 2007
    Location
    Republic of south africa
    Age
    49
    Posts
    184
    Rep Power
    20

    Re: bitzer screw pack help please

    Hi,

    Much as I am interested in knowing the same thing as Brian wants to know I think what you need now are the corrective measures to get your system up and running again. In this case Mad fridgie's method will be an option to seriously consider. To be honest I do not forsee you using the same old moisture contaminated gas and get away with it like that. If you want to simplify things just thouroughly dry the system and induce a fresh charge.

    I had a similar problem begining of this year with an old R22 chiller which raptured its tubes when an antifreeze thermostat failed. Believe me the only way out is to dry out the system thoroughly with dry air and dry Nitrogen. Use your moisture indicators correctly before you even think of charging the system again.

    Best of chances with this one Bru.

  5. #5
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: bitzer screw pack help please

    Suggest everything as per Mad Fridge, and in addition remove the screw compressor and bake in an oven for a week at +80.0 'C under vacuum. Plus invest in a digital vacuum gauge before adding new refrigerant.

  6. #6
    Join Date
    Dec 2010
    Location
    Yorkshire
    Posts
    26
    Rep Power
    0

    Re: bitzer screw pack help please

    thank you for your comments guys the system had 3 vac pumps attached for a period of 24 hours and the torr gauge on my vac pump had reached a suitable level that was when we decided the system was fit to be charged. we also thought that due to the water being off for 4 weeks that the possibility of the leak pulling the water in was slim. we noticed the problem when charged with refrigerant because the system stages up and down on pressure through each compressor and unloading valve and we could not get more than 1 compressor to run at 50%.

    when recovering the refrigerant could we not run it through filters to the bottles and then back through filters when re charging?

    thanks for your comments guys all help is appreciated.

  7. #7
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: bitzer screw pack help please

    The refrigerant is not re-usable. Driers will not separate free water, add the chemical reaction in refrigerant with water. Start with fresh charge after clean up.

Similar Threads

  1. Bitzer Screw Compressor
    By rejan in forum Refrigeration Books
    Replies: 10
    Last Post: 18-04-2010, 08:55 PM
  2. Types of oil lubrication in bitzer screw comp
    By sadiq in forum Industrial Compressors
    Replies: 1
    Last Post: 27-03-2010, 10:42 PM
  3. Bitzer Screw Compressors
    By Davezz in forum Industrial Compressors
    Replies: 9
    Last Post: 09-02-2008, 09:32 PM
  4. bitzer screw compressor
    By joe magee in forum Supermarket Refrigeration
    Replies: 5
    Last Post: 14-01-2007, 01:30 AM
  5. bitzer screw compressor
    By Tejbir Singh in forum Industrial Compressors
    Replies: 3
    Last Post: 18-08-2006, 06:12 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •