geothermal under floor heating
heat pump registered a fault, 701 error low pressure..
this after been gased about 3 weeks ago! anybody any soloutions ASAP???
-
24-12-2010, 11:09 PM #2
Re: geothermal under floor heating
Could be gas again , could be a blockage,faulty lp switch,. What's the make and model??
Is the brine mixture ok,ie. not freezing. Are all pumps running,
StuLast edited by stufus; 24-12-2010 at 11:21 PM.
Tool's ? check ! Condom's ? check !
If you can't fix it , f*ck it !!!
-
29-12-2010, 06:48 AM #3
Re: geothermal under floor heating
If this is a geothermal heat pump please check are the ground heat exchangers sized correct. If the temperatures to the ground are below and around zero, the HE capacity is less than it is needed. Check the temperatures, the flows and than come back. If you have a HP selection sheet, post it so i will check.
BRBe careful about reading health books. You may die of a misprint.
-
30-12-2010, 05:18 AM #4
Re: geothermal under floor heating
Please describe your ground source for heat pump