    hi everyone this is my first thread
    the problem i have is this i have a couple of bottle coolers in our service room from pubs that we have changed the compressors on both are
    r134a but they wont come bellow 12degrees celcius the suction pressure is 4bar and high side 15 the condenser is not blocked the fans all work and the evaporator plate frosts all over we have changed the compressor on one twice and vacked overnite but still the same problem any reply much appreciated



  2. #2
    Join Date
    Jan 2003
    Location
    East Anglia
    Posts
    1,160
    Rep Power
    25

    Re: need help

    Hi Sean1,

    Sounds like they are overcharged, was the gas weighed in.

    Most bottle coolers blow compressors because they are stuck under counters with no airflow.

    Personally i would reclaim the gas, change drier, vac out and regas weighing it in.

    Should sort the problem out

    Regards

    Fatboy

  3. #3
    Join Date
    Oct 2004
    Location
    Scotland
    Age
    46
    Posts
    1,454
    Rep Power
    21

    Re: need help

    Hi Sean

    I would have to agree with fatboy, it sounds like it`s overcharged......... maybe because the capillary is blocked??

    Check cap, change drier and weight the gas in
    IF AT FIRST YOU DON`T SUCCEED.
    DESTROY ALL EVIDENCE THAT YOU TRIED!
    and go get a cuppa

  4. #4
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need help

    cheers guys the gas was nt weighed in they were filled by comparing temp and pressure we did remove some gas but they still had the same problem i will try what you suggested hopefully it will sort it out it really buggin me now

  5. #5
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need help

    hi guys done what u sugested u were right found block in cap was able to unblock using ofn thanks 4 ur help

  6. #6
    Join Date
    Sep 2003
    Location
    ISRAEL
    Age
    72
    Posts
    4,248
    Rep Power
    46

    Re: need help

    Hi sean1,

    Make it a regular check on systems run on 134, to always check the cap tube as they tend to get blocked very quick.


    Chemi

  7. #7
    Join Date
    Jul 2005
    Location
    luton
    Age
    42
    Posts
    87
    Rep Power
    19

    Re: need help

    cheers chemi what makes it more likely on a r134a systems is it just to do with the properties of the refrigerant?