    Dec 2010
    South Africa
    48
    5
    Carrier 30GX please help
    Hi guys i am new to this forum and looking forward to a lot of Q and A.
    I am working on a Carrier 30GX, on the display it shows "override". Only one compressor is running. I had a look in the manual and it says Limit: The operation conditions do not allow total unit operation. Can anyone please tel me what i should be looking for?
    4,697
    Re: Carrier 30GX please help
    Hi Morne and welcome to the forum.
    Please refer to the attached pdf.
    Read section 5.8
    Which is an explanation of your issues.
    Dec 2010
    South Africa
    48
    5
    Hi thank you for your reply. I had a look at that section, i looked on the chiller setpoint menu 2 (no5) and it is set to 100%. I also looked at inputs menu 2 (no4) and found this contact to be open. On the connection terminal no73 and no74 is not connected.
    4,697
    Hi Morne.
    Is this errant chiller stand alone or is it normally ran via CCN.
    Also what version of Prodialog do you have?
    Dec 2010
    South Africa
    48
    5
    Hi it is a stand alone, it only gets a start signal from the bms. I am not sure what vesion prodialog i got.It ran fine for almost 7years now.
    4,697
    If it's that old and stand alone, what I was thinking is redundant.
    Maybe some of the older (and Carrier based) guys on the forum may be able to help?
  1. Replies: 12
  2. Re:We need access codes to the carrier 30gx tell my
    By mikimakx in forum Trouble Shooting
    Last Post: 13-05-2010, 01:27 PM
  3. carrier 30gx oil separator heaters
    By Coolie in forum Trouble Shooting
    Last Post: 12-05-2010, 05:58 PM
  4. Carrier Chiller 30GX Error Code
    By sbkvelocity in forum Trouble Shooting
    Last Post: 07-03-2010, 02:57 AM
  5. Carrier 30GX control issues
    By whoopy-do in forum Trouble Shooting
    Last Post: 03-11-2007, 12:05 AM