Design of compressor
dear all,
ii just want to know the capacity of compressor and its motor size for manufacturing a 32 tos ice from water inlet temp 30'c and ice temp -5 'c at condensing temp is 40'c and evaporation temp of brine tank is -12 'c ...pleasae help or suggese
-
23-12-2010, 12:24 PM #2
Re: Design of compressor
32000 Kg x 35K = 1.120.000 Kcal
Assuming you want to produce 35 tons of ice per day, the average cooling capacity required is 46666 Kcal/h = 54kW.
A suitable compressor with R404A refrigerant would be Z 25 103 Y from Frascold or 6H_25.2Y-40P from Bitzer or equivalent 25HP, 105m3/h compressor from other manufacturers
-
23-12-2010, 01:03 PM #3
Re: Design of compressor
if you are talkin about block ice which i guess , you would roughly need about 35 tons by 1.6 TR compressor .
Alternatively , precool the water from 30 deg c to say 10 , will improve the quality of ice .
-
23-12-2010, 01:16 PM #4
-
23-12-2010, 02:55 PM #5
-
23-12-2010, 07:51 PM #6
Re: Design of compressor
Sounds like the UAE is about to get an ice-rink.
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
25-12-2010, 07:59 AM #7
Re: Design of compressor
Tjank x to all can i use kirlosker compressor Kc 4 model ,flow rate is 580 m3/hr ,
-
25-12-2010, 09:55 AM #8
Re: Design of compressor
Yes, you will freeze the 32 tons of water in 5-6 hours with that compressor @ 1000rpm. But you can't use R404a because the compressor max pressure is 21 bar, so you have to use R134a.
-
26-12-2010, 04:19 PM #9
Re: Design of compressor
thank you
-
22-01-2011, 08:20 PM #10
Re: Design of compressor
how to calcuate refrigeration compressor capacity using its details
Similar Threads
-
AWHP design - suction accumulator
By desA in forum Heat PumpsReplies: 9Last Post: 05-09-2010, 07:53 AM -
Compressor loading, cooling, and range of operation.
By Air duster in forum FundamentalsReplies: 10Last Post: 02-04-2008, 08:39 AM -
Different between compressor MYCOM single stage and compressor booster
By thien nhat in forum CommercialReplies: 7Last Post: 13-12-2007, 06:31 PM -
Mitsubishi compressor lock
By marc5180 in forum Air ConditioningReplies: 29Last Post: 08-10-2007, 05:48 PM -
R507 in an R134a compressor: system design
By DaBit in forum Technical SpeculationsReplies: 17Last Post: 01-05-2003, 09:25 AM