Results 1 to 8 of 8
    Dec 2010
    Iran
    33
    What reason are there for connecting and disconnecting the solenoid valve once per e
    Hi Dear Engineer s association
    Please look at the figure No.1 which is attached .
    This figure is about cntrolling screw compressor capacity.
    There are four solenoid valves in this picture which one of them is connected to capillary tube which is called CR4 and as is mentioned at the catalog that this solenoid valve is had electricity once per 10 seconds .
    now, I have a question (( What reason are there for connecting and disconnecting once per each 10 seconds ?))
    Thank you
    Jun 2009
    North East England
    41
    712
    Re: What reason are there for connecting and disconnecting the solenoid valve once pe
    Possibly oil return/motor cooling
    Jun 2010
    Yorkshire
    59
    520
    Yes definately for oil return to lube the screw meshings.
    3,356
    I think its more for slide valve creeping.
    If at 33,66 or 100% load it pulses every 10 seconds to make sure its at that position.
    Its got nothing to do with lubricating rotors.
    Nov 2010
    London
    624
    15
    Indeed. This also allows the slide valve mechanism to continuously be in relative minute motion reducing the likely hood of seizing in position.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
    Auckland
    74
    3,357
    37
    As per Ranger1 said, pulse loading the capacity slide as required, saves massive loads on drive motor.
    Dec 2010
    Iran
    33
    Thanks for your kind attention.
    Any more comments are welcome.
    Jan 2010
    Christchurch
    54
    28
    most compressor control circuts will pulse the solenoid to ensure it stays at that position, I haven't personabley seen it done at any position lower than 100% but it wouldn't hurt, if the teflon seal leaks a bit of oil past it, the compressor will slowly unload, so if the solenoid is pulsed it will maintain the same position