    What reason are there for connecting and disconnecting the solenoid valve once per e



    Hi Dear Engineer s association

    Please look at the figure No.1 which is attached .
    This figure is about cntrolling screw compressor capacity.
    There are four solenoid valves in this picture which one of them is connected to capillary tube which is called CR4 and as is mentioned at the catalog that this solenoid valve is had electricity once per 10 seconds .
    now, I have a question (( What reason are there for connecting and disconnecting once per each 10 seconds ?))
    Thank you
    Attached Images Attached Images



  2. #2
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: What reason are there for connecting and disconnecting the solenoid valve once pe

    Possibly oil return/motor cooling

  3. #3
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: What reason are there for connecting and disconnecting the solenoid valve once pe

    Yes definately for oil return to lube the screw meshings.

  4. #4
    Join Date
    Dec 2007
    Location
    australia
    Posts
    3,357
    Rep Power
    39

    Re: What reason are there for connecting and disconnecting the solenoid valve once pe

    I think its more for slide valve creeping.
    If at 33,66 or 100% load it pulses every 10 seconds to make sure its at that position.
    Its got nothing to do with lubricating rotors.

  5. #5
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: What reason are there for connecting and disconnecting the solenoid valve once pe

    Quote Originally Posted by RANGER1 View Post
    I think its more for slide valve creeping.
    If at 33,66 or 100% load it pulses every 10 seconds to make sure its at that position.
    Its got nothing to do with lubricating rotors.
    Indeed. This also allows the slide valve mechanism to continuously be in relative minute motion reducing the likely hood of seizing in position.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: What reason are there for connecting and disconnecting the solenoid valve once pe

    As per Ranger1 said, pulse loading the capacity slide as required, saves massive loads on drive motor.

  7. #7
    Join Date
    Dec 2010
    Location
    Iran
    Age
    33
    Posts
    16
    Rep Power
    0

    Re: What reason are there for connecting and disconnecting the solenoid valve once pe

    Thanks for your kind attention.

    Any more comments are welcome.

  8. #8
    Join Date
    Jan 2010
    Location
    Christchurch
    Age
    54
    Posts
    28
    Rep Power
    0

    Re: What reason are there for connecting and disconnecting the solenoid valve once pe

    most compressor control circuts will pulse the solenoid to ensure it stays at that position, I haven't personabley seen it done at any position lower than 100% but it wouldn't hurt, if the teflon seal leaks a bit of oil past it, the compressor will slowly unload, so if the solenoid is pulsed it will maintain the same position