    Would like to know the correct procedure for flushing and cleaning stainless steel plate heat exchangers.

    We have a WP24-14 plate GEA plate heat exchanger, operating now for 5 years as a condenser on a heatpump. Recently it has been noticed that head pressure has been increasing. It is suspected that a film of scale/scum have formed on the heat exchangers plate surfaces ( water side), this is inhibiting the heat transfer to the water. Water flow rate through the condenser is ok.

    Have been told Citric Acid or Formic acid can be used to clean and flush stainless Steel plate heat exchangers.

    Would appreciate any information on this topic.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: Cleaning/Flushing Stainless Steel Plate Heat Exchangers

    Came across this, may be useful...

    http://www.kamco.co.uk/GuidanceNotes...Exchangers.pdf
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Cleaning/Flushing Stainless Steel Plate Heat Exchangers

    Excellent post Brian_UK

  4. #4
    Join Date
    Dec 2010
    Location
    ZA
    Posts
    157
    Rep Power
    16

    Re: Cleaning/Flushing Stainless Steel Plate Heat Exchangers

    Citric Acid will work, and will dissolve scale. Using a strong acid ( sulphuric or hydrochloric) is not recommended, especially HCl, as this will cause severe chloride corrosion inside the heat exchanger, especially in joints and where plates meet. I generally use Absorbic acid, as it is, for me, readily available, and makes a good descaler, especially as I have aluminium plate heat exchangers that tend to corrode internally with plain water. If the water output is in any way going to be used directly by humans ( washing or showering) then rinsing after descaling is a good idea..

Similar Threads

  1. Failure of Stainless Steel Heat Exchanger
    By kiamaian in forum Trouble Shooting
    Replies: 9
    Last Post: 19-10-2010, 11:01 AM
  2. Replies: 5
    Last Post: 14-09-2009, 07:33 AM
  3. Standards rating for Brazed Plate Heat Exchangers
    By Carlos Barrantes in forum Refrigeration Books
    Replies: 0
    Last Post: 17-02-2009, 11:29 PM
  4. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM
  5. Titanium Flat Plate Heat Exchangers
    By TBFTL in forum Technical Speculations
    Replies: 8
    Last Post: 10-09-2006, 10:47 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •