    Exclamation vrv 3 f3 fault code? need help



    hey guys i recently went to look at a vrv 3 system, an error code came up which was f3 high temperature discharge probe, i down powered the unit and re powered, the fault stil occured. i checked each probe on all 6 compressors and could find no sign of burnt probe, i also did a system run on test mode to see if there was a refrigeration leak, no loss of refrigerant found? what else could this be? all help will be much appreciated.



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: vrv 3 f3 fault code? need help

    And what is temperature of the compressor discharges ?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Dec 2010
    Location
    lytham st annes
    Age
    31
    Posts
    10
    Rep Power
    0

    Re: vrv 3 f3 fault code? need help

    i could only test one compressor as the condensing units went in to defrost mode, discharge was 104 degrees and the suction was 2 below zero? any ideas?

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: vrv 3 f3 fault code? need help

    Fault finding from basic Daikin
    Attached Files Attached Files
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2010
    Location
    lytham st annes
    Age
    31
    Posts
    10
    Rep Power
    0

    Re: vrv 3 f3 fault code? need help

    thanks for that much appreciated, i mean i have checked most of these already its just a really strange fault :s

  6. #6
    Join Date
    Nov 2007
    Location
    London
    Posts
    461
    Rep Power
    17

    Re: vrv 3 f3 fault code? need help

    is it a new installation?

  7. #7
    Join Date
    Dec 2010
    Location
    lytham st annes
    Age
    31
    Posts
    10
    Rep Power
    0

    Re: vrv 3 f3 fault code? need help

    it was installed 2 years ago

  8. #8
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,192
    Rep Power
    60

    Re: vrv 3 f3 fault code? need help

    Maybe a sensor going wobbly when it heats up?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  9. #9
    Join Date
    Jan 2009
    Location
    london
    Posts
    52
    Rep Power
    16

    Re: vrv 3 f3 fault code? need help

    just and idea, Had F3 before when one of the fans was working intermittently,but the other fan was stopping it going out on hp and the discharge temp was going too high causing f3 replaced dodgy fan motor and no more faults.
    good luck

  10. #10
    Join Date
    Mar 2010
    Location
    England
    Posts
    41
    Rep Power
    0

    Re: vrv 3 f3 fault code? need help

    F3 error is generated when the temperature of the compressors reaches either 125 degrees 3 times within 30 mins or 135 degrees is reached. The system attempts to lower the overheat of compressors by using the sub-cooling circuit as liquid injection, and/or in the case of the inverter compressor - Reducing the frequency when 115 degrees is reached and the sub - cooler is unable to reduce the temperature (This is called drooping or stepping down control and can be viewed on the service checker when the control is active).

    If the standard compressors are over heating, these cannot (for obvious reasons) be stepped down in speed, in this instance, they are turned off for 10 minute periods by the software. If the system will not operate or reset, and F3 is constantly shown, resistance measurement of the senor should be taken and also the temperature of the pipe, compare the results to the table in the service manual to check the sensor is reading correctly. If you are unable to judge which sensor for which compressor is causing the issue, try using monitor mode binery 14, the led sequence will tell you (if you follow the correct method) which sensor/compressor is generating the fault. Best of luck

Similar Threads

  1. Mitsi Heavy E57 fault code in Error Log on wired controller
    By back2space in forum Air Conditioning
    Replies: 10
    Last Post: 13-10-2010, 09:24 AM
  2. Mitsubishi 1500 fault code fault
    By pie man in forum Air Conditioning
    Replies: 9
    Last Post: 06-05-2010, 09:30 PM
  3. Sanyo Text Back Fault Code Service
    By techguy in forum Air Conditioning
    Replies: 1
    Last Post: 04-02-2009, 07:57 PM
  4. mitsubishi city multi fault code
    By robin r33 gtr in forum Air Conditioning
    Replies: 5
    Last Post: 05-11-2007, 11:23 PM
  5. UA Daikin Fault Code
    By jedi in forum Air Conditioning
    Replies: 2
    Last Post: 23-07-2007, 01:44 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •