Results 1 to 10 of 10
20-12-2010, 06:10 PM #1
Brazing copper to steel accumalator ??
Mitsibushi PU-P1.6VGAA . I was called out to this unit fault today and dignosed a couple of pinhole leaks on top of the accumalator between the factory soldered joint and the accumalator body. I have tried to braze using silver solder and flux but holes keep reappearing. Am i wasting my time trying to braze steel & copper ? or is there another fix. Replacing the accumalator looks like a major pain.
20-12-2010, 06:40 PM #2
Re: Brazing copper to steel accumalator ??
Clean the area to brazed really good, make sure no pressure inside, use 40% silver rods, don't over heat the steel part, it should hardly be orange , it should go nice and easy.
20-12-2010, 06:48 PM #3
If you are really struggling you can pull a slight vac on the unit but be aware that this will pull air into the system and will need a good deep vac pulling before you recharge
20-12-2010, 07:39 PM #4
20-12-2010, 07:48 PM #5
Thanks all, thats helpful. i was using 5% silver rods today.
20-12-2010, 10:52 PM #6
File out the pin holes to remove the impurity and use 40% easiflo rod and flux.
21-12-2010, 12:06 AM #7
I normally start buy burning of the paint (not to much heat) wire wool the area, then wipe down with a damp cloth (water or a solvent) Nice and clean.
I do not on the first instance go directly for the penetration, I "tin" some solder around the area (like a polo) again do not apply to much heat to one area. I then built up the solder from the tinned area to the place of penetration. i find that this does help with the flux penetration and adds extra stenght to the whole joint. (PS I do lke a shoulder of solder as well)
Trick not a hot flame, but a bigger flame covering a greater area
21-12-2010, 02:29 AM #8
21-12-2010, 06:21 AM #9
As chemi said 40% rods and not to hot
21-12-2010, 10:08 AM #10
Repairing a Copper to Steel Brazed Joint.
By Grizzly in forum Trouble ShootingReplies: 14Last Post: 20-02-2010, 10:23 PM -
copper or steel
By mbc in forum Trouble ShootingReplies: 13Last Post: 23-10-2009, 03:34 PM -
zinc coated copper capillary brazing
By bujas in forum Technical DiscussionsReplies: 4Last Post: 18-06-2007, 09:11 PM -
Brazing copper pipe
By Lowrider in forum Technical DiscussionsReplies: 3Last Post: 25-05-2007, 05:12 PM -
titanium and copper/brass/or stainless steel brazing?
By vinay in forum Trouble ShootingReplies: 4Last Post: 08-08-2002, 06:14 PM