    dalkin altherma heat problems



    hi
    i have an dalkin altherma 16 system installed in conjuction with alurad radiators.

    problem is i have my system set to 30deg but the radiators are practically cold. when i turn it to max 55 deg the rads heat the house well.

    currently water temp is 25.4, temp outside is -0.5, system set to 30deg.
    rad temp is slightly warm/cold (even turned off 8 rads in the house)
    i dont have internal thermostat.

    any ideas??
    thanks in advance



  2. #2
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: dalkin altherma heat problems

    Set the heating set point to 55 on the controller.

  3. #3
    Join Date
    Dec 2010
    Location
    ireland
    Posts
    2
    Rep Power
    0

    Re: dalkin altherma heat problems

    hi frank tnx for the fast response.

    went into field function to no 9.00 (heating set point ranges) 00 was set at 55deg
    01 was set at 25 but i changed it to its max of 37deg.
    is that correct?

  4. #4
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: dalkin altherma heat problems

    I didn't mean for you to alter the Service Codes. Once these have been set by the commissioning engineer they should not need changing
    Has the system been properly commissioned?

  5. #5
    Join Date
    Jul 2010
    Location
    Sussex, England
    Age
    50
    Posts
    5
    Rep Power
    0

    Re: dalkin altherma heat problems

    Reset the service settings back to where they were originally set at because changing these will cause no end of problems

    Check the design spec of the system and radiators on it, they should have been sized with a dedicated flow temp, most heat pump design temps will be set with a flow temp of 45 degrees, but the design You have may be different

    If you need any help with the settings let me know as we are a Daikin service agents

    Stuart

Similar Threads

  1. Problems with LG split heat pump M/N LS902hpv
    By joshbloomberg in forum Heat Pumps
    Replies: 5
    Last Post: 08-12-2010, 05:10 PM
  2. System sizing for heat and manual J
    By Larry2 in forum Heat Pumps
    Replies: 5
    Last Post: 25-06-2008, 10:58 AM
  3. Heat transfer coefficient - Coolpack
    By Graham in forum Fundamentals
    Replies: 10
    Last Post: 28-05-2008, 01:08 AM
  4. Poor Heat Exchangers
    By alireza in forum Trouble Shooting
    Replies: 9
    Last Post: 21-03-2007, 08:51 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •