    How to calculate the COP of chiller



    how can I calculate the value of COP for chiller?I have the data of chiller RT, ice cell & building RT, power consumption for chiller, ice cell tonnage and total kilowatt..but I dont know which one I need to take to make the ratio, between the cooling capacity in RT to the energy consumed by the whole chiller in KW..please anybody help me..



  2. #2
    Join Date
    Aug 2007
    Location
    Gosport
    Age
    64
    Posts
    26
    Rep Power
    0

    Re: How to calculate the COP of chiller

    isn't the formula for: - COP = RE/CWD

    refrigerating effect/compressor work down

    You may need an enthalpy chart to calculate or am I missing something

  3. #3
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: How to calculate the COP of chiller

    Quote Originally Posted by hafiz1985 View Post
    how can I calculate the value of COP for chiller?I have the data of chiller RT, ice cell & building RT, power consumption for chiller, ice cell tonnage and total kilowatt..but I dont know which one I need to take to make the ratio, between the cooling capacity in RT to the energy consumed by the whole chiller in KW..please anybody help me..

    COP is a theoretical calculation using Ph charts and needs specific information to work it out.

    You need to know evap and discharge pressures (temps) and include superheat from evap and subcooling from cond.
    You then plot all the info on a Ph chart (correct refrigerant) and the COP can be worked out by dividing the
    RE (Refrigeration Effect (duty over the evap) ) by the WD (Work Done (energy imparted by the compression process) ).

    Give us the refigerant, discharge and suction pressures, include superheat and subcooling and I (we) will show you how.

    All the best

    coolrunnings

    .

  4. #4
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: How to calculate the COP of chiller

    I'm not sure what you are asking for?

    It sounds like you have ice storage?

    I have attached a little spreadsheet I use for comparing between chillers when I am consulting or when I am selecting for my own projects.
    Attached Files Attached Files
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

Similar Threads

  1. process chiller help
    By talon771 in forum Industrial
    Replies: 8
    Last Post: 12-01-2011, 08:42 PM
  2. Chiller project
    By katsuchiyo in forum Commercial
    Replies: 0
    Last Post: 14-12-2010, 02:35 PM
  3. Problems in r22 chiller design
    By umeshpradhan in forum Technical Discussions
    Replies: 9
    Last Post: 06-07-2010, 10:39 AM
  4. Absorption Chiller VS Mech. Chiller
    By Intern in forum Industrial
    Replies: 20
    Last Post: 30-05-2009, 08:31 AM
  5. Trane CVHE 450 R11 Centrifugal Chiller
    By albertjoseph in forum Air Conditioning
    Replies: 4
    Last Post: 06-10-2008, 03:23 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •