    Re: Minimum discharge pressure for ammonia systems

    Andy,

    Great point. I would like to see the chart as well. I'm sure someone has one for the States.

    We have installed a few systems with the wetbulb sensors.
    It would really only seem to matter if you're operating a large system with a low disch. press. setting, and it was set below the actual saturation corresponding to WB. Mainly in the middle of summer.
    Chicago has a design of 95/78 (not if you refer to the latest ASHRAE, but the NH3 guys still use it) so a corresponding saturation = approx 132# Disch.

    If you did not have the WB feature, the system would try and run more condenser fans/ pumps w/ no avail. as the saturated Disch press. setting was not attainable. Or you can stop a VFD on a condenser fan from driving higher if in fact you have already achieved the WB/ Saturation.

    I'll have to look into the Sabroe system.
    This sounds very interesting.
    I'll forward the link for this site to Greg @ M&M to see if he knows anything about it.

    It's great too see so many technicians & engineers involved with this site!!

    Cheers
    Mark.

    I'll introduce myself if I see you at IIAR
    Last edited by Mark Sanchez; 05-01-2007 at 12:51 AM.

Similar Threads

  1. Liquid Overfeed Systems
    By US Iceman in forum NH3
    Replies: 151
    Last Post: 08-03-2007, 05:34 AM
  2. TEV range & minimum pressure diff issue
    By Lc_shi in forum Fundamentals
    Replies: 2
    Last Post: 24-04-2006, 04:32 PM
  3. Energy Savings
    By arkay in forum Industrial
    Replies: 6
    Last Post: 17-03-2006, 12:36 PM
  4. Building a wine cabinet
    By Rory in forum Technical Discussions
    Replies: 38
    Last Post: 13-07-2004, 08:28 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •