Re: Minimum discharge pressure for ammonia systems
Frequency of defrosting is another important factor of refrigeration plant optimization. Right now, here in Ontario, one cold storage has defrosting once per week, but another one has defrosting twice per day. I found that overdefrosting is common problem for many refrigeration plants. It is difficult to justify additional compressor installation, if you have defrosting once per week.
What Sergei mentions about defrosts going from twice per day to once per week has become quite typical in plants that incorporate smarter controls and/or keener operators. Evaporators that require 2 defrosts per day during that one hot week in august can often get away with one or two defrosts during the winter months. This gets back to the problem of fixed setpoints often being the “worst case” setpoint. If two or three defrosts are needed in the summer, that’s where the pins are left in the time clock. If -25 suction kept the rooms cold in August, that’s where the suction is left all year. If one evaporator requires 145# for defrost, that’s where the pressure switches are set. It’s obvious that a lot of systems have a lot of room for energy usage improvements
Another great up-side to long durations between defrosts is you can float the head pressure lower for a longer period of time thus enhancing energy savings.
Brad
-
11-01-2007, 04:57 PM #2
Re: Minimum discharge pressure for ammonia systems
Originally Posted by Bradford
-
11-01-2007, 05:08 PM #3
Re: Minimum discharge pressure for ammonia systems
Originally Posted by Bradford
I continue to believe the system can be designed better and more flexible. The control systems actually provide the ability to sustain the original design concepts with the capability of smarter operation.
One other important criteria is the utility bills, i.e., how much energy and demand cost, the various time of use charges, and ratchet clauses can also present some challenges.
-
14-01-2007, 04:36 AM #4
Re: Minimum discharge pressure for ammonia systems
recip plant on vfd ( im giving my tricks away) :P
-
15-01-2007, 04:14 AM #5
Similar Threads
-
Liquid Overfeed Systems
By US Iceman in forum NH3Replies: 151Last Post: 08-03-2007, 05:34 AM -
TEV range & minimum pressure diff issue
By Lc_shi in forum FundamentalsReplies: 2Last Post: 24-04-2006, 04:32 PM -
Energy Savings
By arkay in forum IndustrialReplies: 6Last Post: 17-03-2006, 12:36 PM -
Building a wine cabinet
By Rory in forum Technical DiscussionsReplies: 38Last Post: 13-07-2004, 08:28 PM