19-12-2010, 02:39 PM #1
fault on ingersoll rand dryer
Hi guys
Got a ingersoll rand dryer with compressor constant running and very hot , thought it was short of gas (r407c) so reclaimed and got 1.7kg should have 2.4kg tried to put new charge in but unit only pulling in 1.8kg wont take any more and comp doing same.
I think comp has gone its not pumping 100% piston failure would i be right to think this, complaint is water down lines on compressed air unit.
any help grateful , cheers
-
19-12-2010, 03:17 PM #2
Re: fault on ingersoll rand dryer
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
-
19-12-2010, 03:20 PM #3
Re: fault on ingersoll rand dryer
hi paul ,
you said you got 1.7 kg of gas out of the system , did you vac out? I take it you pressure tested? how much water did you get out ?
you say the comp, is running very hot, is there any water in it? sedgy
-
19-12-2010, 06:31 PM #4
Re: fault on ingersoll rand dryer
If it`s not got the correct charge that could account for the comp running hot. Don`t rely on the pump pulling in the refrigerant, you`ll need to heat the cylinder with a heat band in this weather to raise the pressure (you`ll be charging as a luquid of course). As DT asks, check the condensate drains. If they`re the Domnick Hunter electronic level detector type they could be faulty (check for a green flashing LED on the drain body, it shows it`s trying to clean itself but it rarely works).
Oh, best to check that some numpty`s not opened the bypass, I`ve lost count how many times I`ve gone site only to find the dryer bypassed
-
20-12-2010, 08:38 PM #5
Re: fault on ingersoll rand dryer
if the unit has hot gas valve keeping suction pressure higher than cylinder pressure you may need to lower pressure or increase cylinder pressure did you find leak to account for short of gas
-
22-12-2010, 06:16 PM #6
Re: fault on ingersoll rand dryer
Hi Martin
Did check and found no leak also drain ok and hot bypass valve ok, the unit is a free standing dryer. comp very hot and running constant just thinking it not pumping 100%,what do u think
-
22-12-2010, 07:26 PM #7
Re: fault on ingersoll rand dryer
Close the suction valve and check if the compressor holds the pressure. If not, replace it.
All driers with HGBP run constantly. did you check the heat exchanger for a leak? It can happened and refrigerant goes into the compressed air system, can be checked easily by holding your leak detector if the air stream.
What component operates the HGBP? Is it a pressure control?
-
22-12-2010, 07:49 PM #8
Re: fault on ingersoll rand dryer
Just been thinking about this, if the dryers in a very cold (and where isn`t at the moment!) and maybe draughty environment the HGBV will try to keep the low pressure from dropping to low by shunting HP gas into the LP side . This will, of course, be hot and as the compressor is cooled by the suction gas it can run very hot if the HGBV is over compensating for very low suction pressure. I`ve had several cases of the compressor cooking itself because of this
Try blocking the condensor with cardboard and see how it goes.
-
22-12-2010, 08:54 PM #9
Re: fault on ingersoll rand dryer
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
-
22-12-2010, 09:53 PM #10
Re: fault on ingersoll rand dryer
Just to clarify what I meant - head pressure control is required purely to maintain TEV capacity. When installing head pressure control we of course do not also need to install hot gas bypass. But when we need to install hot gas bypass then we must be sure to maintain TEV capacity thus we must also install head pressure control when installing hot gas bypass - always.
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
-
23-12-2010, 08:27 PM #11
Re: fault on ingersoll rand dryer
Thanks for reply guys , i am very grateful for your help.
cheers.
Similar Threads
-
vrv3 au fault
By transit 1 in forum Air ConditioningReplies: 6Last Post: 04-11-2010, 10:19 PM -
Mitsubishi 1500 fault code fault
By pie man in forum Air ConditioningReplies: 9Last Post: 06-05-2010, 09:30 PM -
Supra common fault - usually misdiagnosed.
By carrier_trained in forum TransportReplies: 3Last Post: 15-04-2010, 08:56 PM -
Fault with Tango cassette
By airefresco in forum Air ConditioningReplies: 8Last Post: 19-09-2007, 08:42 AM -
UA Daikin Fault Code
By jedi in forum Air ConditioningReplies: 2Last Post: 23-07-2007, 01:44 PM