    Error Code U2



    Installed a new Mitsubishi Electric A/C unit, Outdoor model no. PUHZ-P140VHA3.... unit runs for a few minutes on heating mode and then goes on standby and then back to heating... discharge pressure seems to rise very quick to approx 26/28 bar... controller then shows up fault code U2... calling back to site on monday morning and looking for help on what steps i should carry out first to find the problem...
    all help greatly appreciated...



  2. #2
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Error Code U2

    Off the top of my head U2 is abnormal discharge temp.
    If its a new install check the obvious first,
    Did it require additional refrigerant for pipe run ?
    Was refrigerant added in correct quantity ?
    Are both Valves open?
    Was it pressure tested and vacced correctly ?
    Does it run in cooling test mode?

    Just a few suggestions

    Best of luck

    Stu

  3. #3
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Error Code U2

    This might help you out a bit

    U2
    High discharging temperature
    Abnormal if discharge temperature
    thermistor (TH4) exceeds 125: or 110:
    continuously for 5 minutes.
    Abnormal if during defrosting discharge
    temperature thermistor (TH4) exceeds
    110: continuously for 30 minutes.
    1 Overheated compressor
    operation caused by insufficient
    refrigerant
    2 Defective thermistor
    3 Defective outdoor controller
    board
    4 Defective operation of linear
    expansion valve
    1 Check intake super heat.
    Check leakage of refrigerant.
    Charge additional refrigerant.
    23 Turn the power off and check if U3 is dis-
    played when the power is turned ON again.
    When U3 is displayed, refer to “Judgement
    and action” for U3.
    4 Check linear expansion valve.
    Refer to 8-5.
    U3
    Open/short circuit of discharge
    temperature thermistor (TH4)
    Abnormal if open (3: or less) or short
    (217: or more) is detected during
    compressor operation.
    (Detection is inoperative for 10 seconds to
    10 minutes of compressor starting process
    and for 10 minutes after or during defrosting.)
    1 Disconnection or contact
    failure of connector (TH4) on
    the outdoor controller circuit
    board.
    2 Defective thermistor
    3 Defective outdoor controller
    circuit board
    1 Check connection of connector (TH4) on the
    outdoor controller circuit board.
    Check the lead wire for thermistor (TH4).
    Refer to 8-6.
    2 Check resistance value of thermistor (TH4) or
    temperature on LED display.
    (Thermistor/TH4: Refer to 8-5.)
    (SW2: Refer to 8-7.)
    3 Replace outdoor controller board.

  4. #4
    Join Date
    Jul 2009
    Location
    ireland
    Posts
    15
    Rep Power
    0

    Re: Error Code U2

    Stu

    Its a brand new unit... pipe length is only approx. 12mts... unit was pressure tested and vaccumed out overnight so all ok that way... didnt check unit on cooling mode... had unit on heating mode only as shop was very cold 8 degrees return air temp on controller and outside temp was approx -1 degree.... i take it unit was going on stand-by until it builds up heat....

  5. #5
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Error Code U2

    Hey Aodhan

    Initially the stand-by scenario is to allow coil temp to rise before starting fans.
    But you need a discharge temp in excess of 125c for 5 mins to generate a U2 fault.
    This is just a shot in the dark but did you purge the pipe work through the indoor and back to the outdoor before pressure test to establish a clear circuit IE no blockages ,
    The only reason i ask is on a few occasions ive been called to sites For hp/lp faults to find someone has either kinked a pipe or left one of the flare blanks (bonnets) in place.

    On the otherhand it could be a faulty thermister TH4

  6. #6
    Join Date
    Jul 2009
    Location
    stoke on trent
    Posts
    48
    Rep Power
    0

    Re: Error Code U2

    if it's new check the sensor has not come out of its pipe holder. i've had a few like that, sensor on pipework just above compressor

  7. #7
    Join Date
    Jun 2009
    Location
    Lusk , Dublin
    Posts
    1,115
    Rep Power
    25

    Re: Error Code U2

    If the discharge sensor was out of its pocket it would read a lot lower than the 100 + degrees to trip the unit ,
    Although i do agree with the fact that they regularly turn up out of position ,even disconnected from the board from time to time