    Re: Two stage system troubleshooting



    Quote Originally Posted by DTLarca View Post
    It's not related -
    If your compressors and cap-tubes are right then your problem is as Gary says - oil type and return provisions. This very topic has been discussed before either here on this discussion board or on one of the old Usenet groups - I forget where - but changing the oil type solved the problem.

    I do want to discuss the principle of subcool occurrence with Mad Fridge - but I will start another thread for that - good luck
    OK, I appreciate your reasoning.



  2. #52
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Two stage system troubleshooting

    Quote Originally Posted by Peter_1 View Post
    Nike, add a little bit R134a into the system to rinse the cap tubes. The R134a remains liquid and flushes it.
    Why R410a for the LP?
    I am there simply as possible source of valuable information. To me, it is much more important to gain some general knowledge on two stage cascade.
    I don't have any influence on design and commission.
    My primary goal is to gain some knowledge on cascades from concrete example from life.

  3. #53
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Two stage system troubleshooting

    Quote Originally Posted by Peter_1 View Post
    Nike, add a little bit R134a into the system to rinse the cap tubes. The R134a remains liquid and flushes it.
    Why R410a for the LP?
    I don't know reasoning! I presume that is because of availability.

  4. #54
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Two stage system troubleshooting

    Quote Originally Posted by Gary View Post
    Even the best of oil separators will allow some tiny percentage to pass through. If that oil remains in the evaporator, then over a period of time sufficient oil will accumulate to cause logging problems. For this reason some small amount of oil carrying fluid must be added to ensure oil return, even with a good separator.
    I have advised as you suggested!
    We will see in next few days if advice is accepted.

  5. #55
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Two stage system troubleshooting

    With a good oil separator, only a small amount of oil will be flowing through the evaporator, thus only a small amount of carrying fluid is needed.

    With no separator, large amounts of oil will be flowing through the evaporator, thus large amounts of carrying fluid will be needed... enough to substantially alter the pressure/temperature relationship of the refrigerant, resulting in higher evaporating temperature and higher box temperature.

    Low stage oil return is a serious problem in cascade systems, which must be addressed.

  6. #56
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: Two stage system troubleshooting

    Quote Originally Posted by mad fridgie View Post
    It looks like the sub cooling is only there to reduce the pressure drop across the high stage evap (no direct increase in performance).
    I would expect some reduction in flashing at the interstage, increasing the effective heat transfer surface area... but the same effect could be accomplished by slightly increasing interstage size. I'm thinking the reduced flashing is not worth the added complexity.
    Last edited by Gary; 23-12-2010 at 12:33 AM.

  7. #57
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: Two stage system troubleshooting

    Quote Originally Posted by Gary View Post
    I would expect some reduction in flashing at the interstage, increasing the effective heat transfer surface area... but the same effect could be accomplished by slightly increasing interstage size. I'm thinking the reduced flashing is not worth the added complexity.
    Correct it comes down to how they have selected the heat exchanger

  8. #58
    Join Date
    Oct 2003
    Location
    Belgium
    Age
    62
    Posts
    5,630
    Rep Power
    34

    Re: Two stage system troubleshooting

    In the past, we made several cascades for Meissner coils (R501/R13, R404a/R23 and R1150/R1270) and we still service +/- 20 cascade and autocascades these days. Our experience is that you must have a very, very dry system. The smallest quantity of water in the system will, together with the oil clog your system.
    As Gary said, an oil separator isn't always working 100%
    What's in the Visio file? The same information as in the pdf?
    Is this used as a CPU cooler.
    It's better to keep your mouth shut and give the impression that you're stupid than to open it and remove all doubt.

  9. #59
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Two stage system troubleshooting

    Quote Originally Posted by Peter_1 View Post
    What's in the Visio file? The same information as in the pdf?
    Is this used as a CPU cooler.
    No! It is used as freezer for medical samples.
    File for download is PDF of diagram I made in Visio. That is actual diagram of system with some informations on it.
    I will send you password for download at private message.

    Other PDF is model from Coolpack.

Page 2 of 2 FirstFirst 12

Similar Threads

  1. Two stage ammonia system
    By Samarjit Sen in forum NH3
    Replies: 13
    Last Post: 20-01-2010, 11:47 AM
  2. R404a System Troubleshooting
    By MechEng1 in forum Industrial
    Replies: 30
    Last Post: 11-09-2009, 03:47 PM
  3. Capillary Tube Characteristics
    By Chef in forum Fundamentals
    Replies: 9
    Last Post: 10-03-2009, 01:03 PM
  4. Troubleshooting Mitsubishi Heavy VRV System
    By Cofreth in forum Trouble Shooting
    Replies: 2
    Last Post: 29-08-2006, 05:41 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •