    Question high pressures



    Am using semi-hemertic screw-compressor,BITZER HSN7471-75-40P as carbondioxide chiller,refrigerant isR404A.Cooling water temp.74.4F,liquid line temp.75.02F,liquidline after ecolomizer(sub-cooler)temp.69.44F,pressure after filter drier18.4bar,press before filter18.5bar,discharge press 18.6bar,Disch.Temp.167.54F,suction press.1.1bar,suct.temp.-11.38F.Pliz help me solve high discharge pressures?



  2. #2
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: high pressures

    What is temperature in and out of cooling water circuit?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  3. #3
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: high pressures

    Com'n Brian... read the post

    Cooling water temp.74.4F

  4. #4
    Brian_UK's Avatar
    Brian_UK is offline Moderator I am starting to push the Mods: of RE Site Moderator : and general nice guy
    Join Date
    Mar 2001
    Location
    Dorset
    Age
    76
    Posts
    11,025
    Rep Power
    60

    Re: high pressures

    I know, I saw that, but which way was it going when got that hot?
    Brian - Newton Abbot, Devon, UK
    Retired March 2015

  5. #5
    Join Date
    Dec 2010
    Location
    Greece
    Posts
    15
    Rep Power
    0

    Re: high pressures

    Quote Originally Posted by juma View Post
    Am using semi-hemertic screw-compressor,BITZER HSN7471-75-40P as carbondioxide chiller,refrigerant isR404A.Cooling water temp.74.4F,liquid line temp.75.02F,liquidline after ecolomizer(sub-cooler)temp.69.44F,pressure after filter drier18.4bar,press before filter18.5bar,discharge press 18.6bar,Disch.Temp.167.54F,suction press.1.1bar,suct.temp.-11.38F.Pliz help me solve high discharge pressures?
    the filters in liquid line need change.

  6. #6
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,357
    Rep Power
    37

    Re: high pressures

    At 1.1bar suction pressure either the TXV is faulty, or if fitted the danfoss suction strainer has collapsed and restricting suction flow to compressor.
    magoo

  7. #7
    Join Date
    Apr 2001
    Location
    New Port Richey, Florida - USA
    Age
    79
    Posts
    5,071
    Rep Power
    35

    Re: high pressures

    Looks like overcharge to me.

  8. #8
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: high pressures

    24°C entering condenser, I assume 29°C leaving, 34°C condensing that is 15.6 bar for R404a.
    My try: the condenser is filthy and probably overcharged. 10k of subcooling is a lot.

  9. #9
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: high pressures

    First indication is overcharge, but look at the economiser temp, this is not operating correctly, this would cause incorrect flow through the exapansion valve, possibly backing up liquid in the condensor, giving the effect of overcharge (near flooded, lots of sub cooling and elevated pressure)

  10. #10
    Join Date
    Mar 2006
    Location
    Merate (LC) - Italy
    Age
    53
    Posts
    2,549
    Rep Power
    24

    Re: high pressures

    Yes, I assumed the subcooling is net of economiser.
    Otherwise is probably just a filthy or clogged condenser.

  11. #11
    Join Date
    Aug 2009
    Location
    New Zealand
    Age
    60
    Posts
    2,554
    Rep Power
    26

    Re: high pressures

    If this a shell tube evap (refrigerant on the shell side) could be flooded or DX, then with the econoniser not in operation, a large % of the volume of the shell will be taken up with excess flash gas (passing through the liquid), the liquid which has been replaced with excess flash gas must be held within the condensor, decreasing condensing surface area and increasing sub cooling surface area.
    I would expect the liquid after the econ heat exchanger to be closer to 0C (32F)

Similar Threads

  1. daikin inverter high pressures!
    By totalacedude in forum Air Conditioning
    Replies: 6
    Last Post: 27-05-2010, 09:31 PM
  2. Over charged system... what symptoms?
    By Clk320_Greg in forum Trouble Shooting
    Replies: 2
    Last Post: 19-10-2009, 06:25 PM
  3. High suction and liquid pressures
    By bth0mas20 in forum Trouble Shooting
    Replies: 4
    Last Post: 28-08-2009, 08:32 PM
  4. High pressures ...vapour and liquid...
    By marco59 in forum Air Conditioning
    Replies: 0
    Last Post: 10-06-2009, 09:51 PM
  5. Compressor Pressures at High Ambient Air
    By Andreas11 in forum Air Conditioning
    Replies: 16
    Last Post: 18-04-2008, 09:28 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •