Thread: high pressures
-
17-12-2010, 09:31 AM #1
high pressures
Am using semi-hemertic screw-compressor,BITZER HSN7471-75-40P as carbondioxide chiller,refrigerant isR404A.Cooling water temp.74.4F,liquid line temp.75.02F,liquidline after ecolomizer(sub-cooler)temp.69.44F,pressure after filter drier18.4bar,press before filter18.5bar,discharge press 18.6bar,Disch.Temp.167.54F,suction press.1.1bar,suct.temp.-11.38F.Pliz help me solve high discharge pressures?
-
17-12-2010, 08:07 PM #2
Re: high pressures
What is temperature in and out of cooling water circuit?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
17-12-2010, 10:17 PM #3
Re: high pressures
Com'n Brian... read the post
Cooling water temp.74.4F
-
17-12-2010, 11:21 PM #4
Re: high pressures
I know, I saw that, but which way was it going when got that hot?
Brian - Newton Abbot, Devon, UK
Retired March 2015
-
22-12-2010, 11:19 PM #5
-
23-12-2010, 12:07 AM #6
Re: high pressures
At 1.1bar suction pressure either the TXV is faulty, or if fitted the danfoss suction strainer has collapsed and restricting suction flow to compressor.
magoo
-
23-12-2010, 07:25 AM #7
-
23-12-2010, 09:27 AM #8
Re: high pressures
24°C entering condenser, I assume 29°C leaving, 34°C condensing that is 15.6 bar for R404a.
My try: the condenser is filthy and probably overcharged. 10k of subcooling is a lot.
-
23-12-2010, 09:37 AM #9
Re: high pressures
First indication is overcharge, but look at the economiser temp, this is not operating correctly, this would cause incorrect flow through the exapansion valve, possibly backing up liquid in the condensor, giving the effect of overcharge (near flooded, lots of sub cooling and elevated pressure)
-
23-12-2010, 12:16 PM #10
Re: high pressures
Yes, I assumed the subcooling is net of economiser.
Otherwise is probably just a filthy or clogged condenser.
-
23-12-2010, 08:57 PM #11
Re: high pressures
If this a shell tube evap (refrigerant on the shell side) could be flooded or DX, then with the econoniser not in operation, a large % of the volume of the shell will be taken up with excess flash gas (passing through the liquid), the liquid which has been replaced with excess flash gas must be held within the condensor, decreasing condensing surface area and increasing sub cooling surface area.
I would expect the liquid after the econ heat exchanger to be closer to 0C (32F)
Similar Threads
-
daikin inverter high pressures!
By totalacedude in forum Air ConditioningReplies: 6Last Post: 27-05-2010, 09:31 PM -
Over charged system... what symptoms?
By Clk320_Greg in forum Trouble ShootingReplies: 2Last Post: 19-10-2009, 06:25 PM -
High suction and liquid pressures
By bth0mas20 in forum Trouble ShootingReplies: 4Last Post: 28-08-2009, 08:32 PM -
High pressures ...vapour and liquid...
By marco59 in forum Air ConditioningReplies: 0Last Post: 10-06-2009, 09:51 PM -
Compressor Pressures at High Ambient Air
By Andreas11 in forum Air ConditioningReplies: 16Last Post: 18-04-2008, 09:28 AM