Results 1 to 5 of 5
-
16-12-2010, 10:03 PM #1
Mitsu R22 Multi Inverter Wiring Diagram Help
dear friends
please take a minute to study the wiring diagram below:
http://rapidshare.com/files/43760585...ng_diagram.pdf
you will note that relays x61, x62, x63 are wired on the neutral.
can anyone explain how these are switched, can't see coils on diagram anywhere
thanksLast edited by Contactor; 16-12-2010 at 10:32 PM. Reason: edit
-
16-12-2010, 11:25 PM #2
Re: Mitsu R22 Multi Inverter Wiring Diagram Help
Coils aren't shown as they are part of the board wiring and not too relevant to the wiring scheme overall.
They respond to sensor inputs and the software drives the relays.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
17-12-2010, 12:07 AM #3
Re: Mitsu R22 Multi Inverter Wiring Diagram Help
they're the fan speed control, fan windings fine, cap is fine, motor is getting power but not turning as these relays all switch motor..
question is how to check coil voltage using this drawing?Last edited by Contactor; 17-12-2010 at 12:08 AM. Reason: edit
-
17-12-2010, 08:11 PM #4
Re: Mitsu R22 Multi Inverter Wiring Diagram Help
About all you can do is take the PCB off the machine base and visually trace the fan wire connector back to a relay.
You might find the relay reference printed on the pcb. There will be a least three relays side by side.Brian - Newton Abbot, Devon, UK
Retired March 2015
-
17-12-2010, 11:58 PM #5
Re: Mitsu R22 Multi Inverter Wiring Diagram Help
As stated these relays would be switched by the PCB - I would imagine from either the states of the HP switches (63H1 on the lower board and 63H2 board on top right) and maybe from one of the thermisters.
If there is a 240V feed on pin 2 and also pin 4 for the capacitor then I would try to find if there was a neutral connection on pins 3, 5 or 6. From there going to the relays to trace the neutral connection back. On the PCB relays hopefully you can get to the soldered terminals to check for a signal voltage with some sharp probes.
Couldn't find a service details relating to the exact unit but a close match here:
http://www.pcug.org.au/training/trai...viceManual.pdf
on page 50 shows a similar motor explaining the wiring arrangements if that helps clarify your testing of the windings.
Cheers,
Andy.Health and safety first..........unless I'm in a hurry.
Similar Threads
-
kfr61 wiring diagram with soft start
By marshy in forum ElectricalReplies: 6Last Post: 08-12-2010, 08:49 AM -
Sigma m series unit wiring diagram
By martin102 in forum ElectricalReplies: 1Last Post: 14-05-2010, 06:28 AM -
York HICA 600 A51 wiring diagram
By RickSter in forum Air ConditioningReplies: 2Last Post: 06-05-2010, 01:23 AM -
Airdale wiring diagram needed
By glenn1340 in forum Heat PumpsReplies: 4Last Post: 12-04-2009, 10:14 PM -
Electrical Wiring Diagram
By bhasadu in forum ElectricalReplies: 0Last Post: 21-06-2008, 09:15 AM