14-12-2010, 09:02 PM #1
Dixell XT110D
I have a Dixell XT110D that was displaying an inaccurate temperature. Assumed the sensor was faulty, ordered correct one (PTC) and changed however is still giving the false reading.
Any ideas?
-
14-12-2010, 11:04 PM #2
Re: Dixell XT110D
Is the unit set for the correct probe type?
Have you calibrated the new probe to the unit?
http://www.dixell.com/linea58/downlo...-111C-D_GB.pdfBrian - Newton Abbot, Devon, UK
Retired March 2015
-
15-12-2010, 07:10 PM #3
Re: Dixell XT110D
put the probe in crushed ice and it should read 0c shimple!
-
20-12-2010, 06:20 PM #4
Re: Dixell XT110D
Hi Brian, thanks for the sheets, these are the same as the ones I had but turns out my controller is an older version, no probe selection parameter (PbC) on this one.
It looks like its the controller itself that is faulty, seems to be out of calibration by quite a bit. New controller on its way.