    Liquid Float Drainers use in Hot Gas Defrost



    Hello everyone,

    What is everyone's thoughts on Liquid Float Drainers and their use in Hot Gas Defrost? Do they work well? What issues should one look out for?

    Any insight is much appreciated as I'm a newbie in the industrial refrigeration arena.

    Regards



  2. #2
    Join Date
    May 2007
    Location
    Auckland
    Age
    74
    Posts
    3,362
    Rep Power
    37

    Re: Liquid Float Drainers use in Hot Gas Defrost

    Hi Redbos.
    welcome to the forum.
    Firstly, hot gas is more like cool gas by the time it reachs the evaporator, with suction pressure regulation etc., the evap becomes a big condenser, so draining excess liquid is necessary. So long as drain valve is sized correctly no problems, oil draining will happen at same time, the oil can clogg up the float and orifice though, and not drain excess liquid. So when system changes over, it can create a flood back.

  3. #3
    redbos's Avatar
    redbos Guest

    Re: Liquid Float Drainers use in Hot Gas Defrost

    So it sounds like if they are installed correctly, they should work well.

    From an energy standpoint, how do Liquid Float Drainers stack up to other methods of defrost?

  4. #4
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Liquid Float Drainers use in Hot Gas Defrost

    the WITT have high pressure float regulators, and are the "HR".
    To make progress is never good enough, I want to do better and better and better

  5. #5
    Join Date
    Sep 2008
    Location
    Canada
    Posts
    811
    Rep Power
    18

    Re: Liquid Float Drainers use in Hot Gas Defrost

    Definitely liquid drainers are better than back pressure regulators, because they drain the liquid and don't pass the gas. Blow by gas will reduce plant efficiency. However, liquid drainers are more expensive than BPRs.

  6. #6
    Join Date
    Dec 2008
    Location
    Portugal
    Age
    48
    Posts
    1,044
    Rep Power
    19

    Re: Liquid Float Drainers use in Hot Gas Defrost

    Quote Originally Posted by Segei View Post
    Definitely liquid drainers are better than back pressure regulators, because they drain the liquid and don't pass the gas. Blow by gas will reduce plant efficiency. However, liquid drainers are more expensive than BPRs.
    Plenty agree with Segei
    To make progress is never good enough, I want to do better and better and better

Similar Threads

  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Replies: 42
    Last Post: 15-01-2011, 02:24 AM
  2. trouble with liquid return after defrost in rack
    By coldkeeper1 in forum Supermarket Refrigeration
    Replies: 12
    Last Post: 18-09-2009, 09:46 PM
  3. liquid return through suction line after hot gas defrost period
    By coldkeeper1 in forum Supermarket Refrigeration
    Replies: 2
    Last Post: 19-06-2008, 10:07 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Replies: 3
    Last Post: 04-08-2005, 03:46 PM

Tags for this Thread

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •