    Hello everyone,
    What is everyone's thoughts on Liquid Float Drainers and their use in Hot Gas Defrost? Do they work well? What issues should one look out for?
    Any insight is much appreciated as I'm a newbie in the industrial refrigeration arena.
    Auckland
    68
    3,362
    32
    Re: Liquid Float Drainers use in Hot Gas Defrost
    Hi Redbos.
    welcome to the forum.
    Firstly, hot gas is more like cool gas by the time it reachs the evaporator, with suction pressure regulation etc., the evap becomes a big condenser, so draining excess liquid is necessary. So long as drain valve is sized correctly no problems, oil draining will happen at same time, the oil can clogg up the float and orifice though, and not drain excess liquid. So when system changes over, it can create a flood back.
    redbos's Avatar
    redbos Guest
    So it sounds like if they are installed correctly, they should work well.
    From an energy standpoint, how do Liquid Float Drainers stack up to other methods of defrost?
    Dec 2008
    Portugal
    42
    1,040
    13
    the WITT have high pressure float regulators, and are the "HR".
    Sep 2008
    Canada
    781
    13
    Definitely liquid drainers are better than back pressure regulators, because they drain the liquid and don't pass the gas. Blow by gas will reduce plant efficiency. However, liquid drainers are more expensive than BPRs.
    Dec 2008
    Portugal
    42
    1,040
    13
    Quote Originally Posted by Segei View Post
    Plenty agree with Segei
  1. Superheat and Subcooling
    By Chunk in forum Fundamentals
    Last Post: 15-01-2011, 01:24 AM
  2. trouble with liquid return after defrost in rack
    By coldkeeper1 in forum Supermarket Refrigeration
    Last Post: 18-09-2009, 09:46 PM
  3. liquid return through suction line after hot gas defrost period
    Last Post: 19-06-2008, 10:07 PM
  4. Parker levels in ammonia systems
    By Friobernal in forum Industrial
    Last Post: 04-08-2005, 03:46 PM
Tags for this Thread