    Hello , today i encounter a weird issue with a carrier chiller plant model # 30hz-101-A0025-PEE
    with a PRO-DIALOG plus Control (white)
    the customer states it's been running for the last year with fault codes for all 4 compressor oil heaters.

    Went and check the heaters and all 4 getting 120V and heating properly when the compressor start the power goes away as normal but after resetting alarms, 10 second after the alarm goes off again in the B compressors or A compressor whichever is running here's the alarms codes:
    606 18=15 13=12 Comp B2 oil heater
    506 18=15 13=12 Comp B1 oil heater
    106 18=14 13=12 Comp A1 oil heater
    206 18=13 13=12 Comp A2 oil heater
    606 5=55 13=12 Comp B1 oil heater
    206 19=19 6=12 Comp A2 oil heater


    Please any help much appreciated....



  2. #2
    Join Date
    Sep 2009
    Location
    Iran
    Age
    66
    Posts
    672
    Blog Entries
    1
    Rep Power
    19

    Re: Carrier 30HZ chiller

    could you mail your Electrical drawing for me might i could help.
    gholbehan@yahoo.com

  3. #3
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,712
    Rep Power
    46

    Re: Carrier 30HZ chiller

    Hi DC5
    Check out your heater circuit as the supply is being interrupted to the heater alarm circuit.
    Pay particular attention to which side of your N/C contacts is being fed.
    The issue is likely to be a wiring fault?
    Good luck Grizzly

  4. #4
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Carrier 30HZ chiller

    cpm/am board check if any have red lights [indicates faulty board] on if the supply chain is faulty it can cause this

  5. #5
    Join Date
    Dec 2010
    Location
    Fl,United States
    Posts
    16
    Rep Power
    0

    Re: Carrier 30HZ chiller

    well its complicated, the system got rearranged from the 4 panel enclosure to half since they installed 4 freq drives so no wiring diagram could be found in vessel ill post pics soon also anyone with a chat service, so can explain more in depth?

  6. #6
    Join Date
    Dec 2010
    Location
    Fl,United States
    Posts
    16
    Rep Power
    0

    Re: Carrier 30HZ chiller

    Quote Originally Posted by mbc View Post
    could you mail your Electrical drawing for me might i could help.
    gholbehan@yahoo.com
    sorry but the electrical wiring is not available by the way this unit is installed in a 58 meters CMN Yacht.
    the engineer can't find any wiring related to the system and the last thing done was 4 freq drives for the compressors and since no space available they relocated all electrical and the controller together in the 2nd half of the enclosure panel so yeah it's a mess here's the pics: (also if any way i can chat with anyone t obet explain the system it's my first time with this system ...






  7. #7
    Join Date
    Dec 2010
    Location
    Fl,United States
    Posts
    16
    Rep Power
    0

    Re: Carrier 30HZ chiller

    Quote Originally Posted by Grizzly View Post
    Hi DC5
    Check out your heater circuit as the supply is being interrupted to the heater alarm circuit.
    Pay particular attention to which side of your N/C contacts is being fed.
    The issue is likely to be a wiring fault?
    Good luck Grizzly
    what do you mean by to which side f your N/C contacs?

  8. #8
    Join Date
    Jun 2009
    Location
    North East England
    Age
    41
    Posts
    712
    Rep Power
    19

    Re: Carrier 30HZ chiller

    What model compressors do you have?

  9. #9
    Join Date
    Jun 2006
    Location
    South Coast
    Posts
    278
    Rep Power
    23

    Re: Carrier 30HZ chiller

    Have these alarms just happened or is this after the rewiring ?

  10. #10
    Join Date
    Sep 2007
    Location
    Somerset
    Age
    69
    Posts
    4,712
    Rep Power
    46

    Re: Carrier 30HZ chiller

    Quote Originally Posted by DC5-T View Post
    what do you mean by to which side f your N/C contacs?
    DC.
    My reasoning behind my question is that.
    On most systems and your may well of been wired like this.
    Crankcase heaters are wired through a normally closed contact either built into the compressor run contactor.
    Or through an axillary contact on the top of it, with a permanent power supply to the input side of the contactor.
    This means that when the compressor is off the crankcase heaters are energised.
    Likewise when they are on the heaters are off.

    With this in mind.
    I was questioning whether the controller was still getting a status signal from these contacts.

    I suspect since your comp drives were converted the board is not getting a signal to either tell it the crankcase heaters are on.

    Or as is more likely it is not getting a signal that they are switched off by the fact that the comp is running.

    This may of been achieved by putting the heater supply through a N/O contact as well as the afore mentioned N/C contacts.

    I think! Something has been missed off during the conversion.

    If you could get a diagram of the inputs and outputs of the controller it all may make sense?
    Grizzly

Similar Threads

  1. Replies: 12
    Last Post: 27-03-2011, 04:12 AM
  2. Carrier chiller 30ra/rh
    By peterbw in forum Trouble Shooting
    Replies: 9
    Last Post: 02-11-2010, 12:46 PM
  3. carrier chiller 30ra/rh trouble shooting
    By peterbw in forum Technical Discussions
    Replies: 0
    Last Post: 24-10-2010, 08:15 AM
  4. Carrier chiller basic board problem
    By noushad123 in forum Trouble Shooting
    Replies: 25
    Last Post: 17-06-2010, 06:55 AM
  5. Carrier Chiller Help
    By superswill in forum Trouble Shooting
    Replies: 7
    Last Post: 18-01-2007, 10:06 PM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •