    Compressor - Maximum Starts per Hour



    Hello!

    Is there a average standard of Maximum Starts per Hour recommended for certain range of size and types of compressors?

    I'd be thankful if you could help me getting some info about it.

    For example: a 10HP reciprocating compressor has Maximum Starts per Hour = 8 (not a real value, just an example).

    Thanks in advanced!
    Last edited by georgedvf; 13-12-2010 at 11:08 PM.



  2. #2
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: Compressor - Maximum Starts per Hour

    Quote Originally Posted by georgedvf View Post
    Hello!

    Is there a average standard of Maximum Starts per Hour recommended for certain range of size and types of compressors?

    I'd be thankful if you could help me getting some info about it.

    For example: a 10HP reciprocating compressor has Maximum Starts per Hour = 8 (not a real value, just an example).

    Thanks in advanced!

    6 starts per hour is what most manufacturers work to..

    coolrunnings

    .

  3. #3
    Join Date
    Jun 2010
    Location
    Yorkshire
    Age
    59
    Posts
    520
    Rep Power
    19

    Re: Maximum Starts per Hour

    Yes there is a guidance note from each motor manufacturer that will give guidance on starting, stopping, and plugin reversal. Usually in the case of fridge and aircon, even on the older systems before soft starts and VVF and DC drives. They used traditional winding configuration, and voltage limit control, transformers, external resistors, and mercury valve rectifiers were quite common with industrial applications. And sometimes the methods were chosen and implemented by the designer/installer, and not always by the manufacturer. And sometimes introducing new starting methods never seen or used before in traditional starting methods.

    When you look at the same problems with compressors, they wil give you the bare minimum starts to edge their bets, due to the expected high starting torque load. This value will differ somewhat with the actual motor characterisitc specification, given by a different manufacturer. For the same size motor that is a stand alone motor that is ready to be coupled to a load.

    You can find and follow a single guide that will be handy to keep in your pocket. Or just go with a particular manufacturers guidance for their products.

    I know a 500 HP 415v 6 pole squirrel cage motor using a traditional star/wye delta, is specified to only have up to seven starts and plugin reverses in an hour. This was specified by Brook Crompton for the coupled load application it was designed for. But they give several other specs for different loads, utilizing the full torque load capabillity of the motor.

    Jaque Hay gave totally different specs for the same size motor, as did Siemens. A lot of the time the specs were ignored, and sometimes the motors burnt out. And sometimes they run for years with no problems. In the case of them being rewound, it depended on which firm did the rewind. And whether it was an emergency rewind, or a non essential one.

  4. #4
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Maximum Starts per Hour

    Thanks, so there's no General considerations??? Do you have some links to where I can find this info of BITZER compressors? I've been looking and can't find it.

  5. #5
    Join Date
    Feb 2010
    Location
    England
    Age
    60
    Posts
    242
    Rep Power
    16

    Re: Maximum Starts per Hour

    Quote Originally Posted by georgedvf View Post
    Thanks, so there's no General considerations??? Do you have some links to where I can find this info of BITZER compressors? I've been looking and can't find it.

    http://www.bitzer.de/eng/products/docu/doc_ov/2

    technical information

    Bitzer say no more than 8 starts an hour.

    coolrunnings

    .

  6. #6
    Join Date
    Nov 2009
    Location
    Minsk, Belarus
    Age
    39
    Posts
    171
    Rep Power
    15

    Re: Maximum Starts per Hour

    Bitzer say no more than 8 starts an hour.
    Exactly.
    Check this
    http://www.bitzer.de/eng/productservice/p4d/KT-100
    In some places will have to think ...

  7. #7
    Join Date
    Feb 2008
    Location
    england
    Posts
    505
    Rep Power
    21

    Re: Maximum Starts per Hour

    6 starts per hour

  8. #8
    Join Date
    Oct 2007
    Location
    Mexico
    Age
    44
    Posts
    158
    Rep Power
    17

    Re: Maximum Starts per Hour

    Thanks to all! The Bitzer link helped a lot!

    Regards.

Similar Threads

  1. Maximum Starting Current
    By weeliang82 in forum Air Conditioning
    Replies: 4
    Last Post: 29-04-2010, 04:15 AM
  2. Lighting circuit trips when heat pump starts
    By mac_J in forum Technical Discussions
    Replies: 4
    Last Post: 08-02-2010, 10:03 PM
  3. Maximum centrifugal fan outlet velocity
    By abbasi in forum Fundamentals
    Replies: 6
    Last Post: 29-11-2008, 06:04 AM
  4. Extra hour in bed
    By monkey spanners in forum Chit Chat & Service Stories
    Replies: 1
    Last Post: 01-11-2006, 11:11 PM
  5. Maximum Discharge Temperature
    By dallan in forum Commercial
    Replies: 6
    Last Post: 13-09-2004, 07:42 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •