Thread: Maximum Starts per Hour
-
13-12-2010, 10:49 PM #1
Compressor - Maximum Starts per Hour
Hello!
Is there a average standard of Maximum Starts per Hour recommended for certain range of size and types of compressors?
I'd be thankful if you could help me getting some info about it.
For example: a 10HP reciprocating compressor has Maximum Starts per Hour = 8 (not a real value, just an example).
Thanks in advanced!Last edited by georgedvf; 13-12-2010 at 11:08 PM.
-
13-12-2010, 11:16 PM #2
-
13-12-2010, 11:47 PM #3
Re: Maximum Starts per Hour
Yes there is a guidance note from each motor manufacturer that will give guidance on starting, stopping, and plugin reversal. Usually in the case of fridge and aircon, even on the older systems before soft starts and VVF and DC drives. They used traditional winding configuration, and voltage limit control, transformers, external resistors, and mercury valve rectifiers were quite common with industrial applications. And sometimes the methods were chosen and implemented by the designer/installer, and not always by the manufacturer. And sometimes introducing new starting methods never seen or used before in traditional starting methods.
When you look at the same problems with compressors, they wil give you the bare minimum starts to edge their bets, due to the expected high starting torque load. This value will differ somewhat with the actual motor characterisitc specification, given by a different manufacturer. For the same size motor that is a stand alone motor that is ready to be coupled to a load.
You can find and follow a single guide that will be handy to keep in your pocket. Or just go with a particular manufacturers guidance for their products.
I know a 500 HP 415v 6 pole squirrel cage motor using a traditional star/wye delta, is specified to only have up to seven starts and plugin reverses in an hour. This was specified by Brook Crompton for the coupled load application it was designed for. But they give several other specs for different loads, utilizing the full torque load capabillity of the motor.
Jaque Hay gave totally different specs for the same size motor, as did Siemens. A lot of the time the specs were ignored, and sometimes the motors burnt out. And sometimes they run for years with no problems. In the case of them being rewound, it depended on which firm did the rewind. And whether it was an emergency rewind, or a non essential one.
-
14-12-2010, 12:00 AM #4
Re: Maximum Starts per Hour
Thanks, so there's no General considerations??? Do you have some links to where I can find this info of BITZER compressors? I've been looking and can't find it.
-
14-12-2010, 12:37 AM #5
Re: Maximum Starts per Hour
http://www.bitzer.de/eng/products/docu/doc_ov/2
technical information
Bitzer say no more than 8 starts an hour.
coolrunnings
.
-
17-12-2010, 07:42 AM #6
Re: Maximum Starts per Hour
Bitzer say no more than 8 starts an hour.
Check this
http://www.bitzer.de/eng/productservice/p4d/KT-100In some places will have to think ...
-
17-12-2010, 07:49 AM #7
Re: Maximum Starts per Hour
6 starts per hour
-
17-12-2010, 05:45 PM #8
Re: Maximum Starts per Hour
Thanks to all! The Bitzer link helped a lot!
Regards.
Similar Threads
-
Maximum Starting Current
By weeliang82 in forum Air ConditioningReplies: 4Last Post: 29-04-2010, 04:15 AM -
Lighting circuit trips when heat pump starts
By mac_J in forum Technical DiscussionsReplies: 4Last Post: 08-02-2010, 10:03 PM -
Maximum centrifugal fan outlet velocity
By abbasi in forum FundamentalsReplies: 6Last Post: 29-11-2008, 06:04 AM -
Extra hour in bed
By monkey spanners in forum Chit Chat & Service StoriesReplies: 1Last Post: 01-11-2006, 11:11 PM -
Maximum Discharge Temperature
By dallan in forum CommercialReplies: 6Last Post: 13-09-2004, 07:42 AM