Thread: Heat Pump Low Pressure Faults
-
12-12-2010, 01:13 PM #1
Heat Pump Low Pressure Faults
During the past couple of weeks in the midst of the cold spell, we have attended several call outs to E4 (low pressure) faults on Daikin splits. Systems on R407C and in heating mode with the coils heavily frosting and not clearing fully on defrost.
Even the one recently fitted in our office was showing E4. I thought that the apprentice had not pressure tested correctly so I got him to recover and re-test, only to find that it was sound with a correct charge!!
Any one else been having these problems?
-
12-12-2010, 01:34 PM #2
Re: Heat Pump Low Pressure Faults
Not me personally but I do know a lot of engineers I associate with have had similar troubles during this recent cold spell
-
12-12-2010, 04:02 PM #3
Re: Heat Pump Low Pressure Faults
Yes we have also had a couple with the most recent being on a Lennox packaged unit that trips as soon as the temperature drops.
I've got a post on here entitled "would a HGB work"The difference between genius and stupidity is that genius has its limits.
Marc
-
12-12-2010, 06:26 PM #4
- Join Date
- Sep 2007
- Location
- Split Croatia
- Age
- 57
- Posts
- 6,151
- Blog Entries
- 6
- Rep Power
- 36
Re: Heat Pump Low Pressure Faults
I think that is possible that during low temperatures R407C somehow fractionate partially (as oppose to R410A) and therefore low pressure alarm. I have that error frequently on air-to-water heat pumps of larger capacity with R407C and they are usually limited to -5°C outdoor air temperature working limit. I personally set them to use electrical backup heater when temperature is -2°C (which is rare in my location).
Last edited by nike123; 12-12-2010 at 06:29 PM.
-
12-12-2010, 08:22 PM #5
Re: Heat Pump Low Pressure Faults
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
-
13-12-2010, 09:01 AM #6
-
13-12-2010, 02:06 PM #7
Re: Heat Pump Low Pressure Faults
Forgot to mention.....
We have also had this happen on a 3 pipe RSEYP8.
-
13-12-2010, 02:07 PM #8
-
17-12-2010, 07:05 PM #9
Re: Heat Pump Low Pressure Faults
I have had a e4 fault code before on a sililar system but the charge was fine, The problem was a defective p.c.b on outdoor unit. I changed the p.c.b and got it back up and running again.
-
17-12-2010, 09:48 PM #10
Re: Heat Pump Low Pressure Faults
could be lp sensor/transducer.get ur gauges on,run it and watch the gauge.if the comp starts to drive the back pressure to where u wanna be then goes into fault its ur faulty lp.check with "technical help desk!"on resistance readings before u change the pcb
-
17-12-2010, 09:53 PM #11
Re: Heat Pump Low Pressure Faults
Looking at some of the replies to this thread, it's obvious that the main point has been missed.
The cold weather has caused the R407C to reduce in pressure below the set point of the LP switch/sensor.
Once the ambient has increased the LP fault goes away, without any loss of charge.
Please re-read the original post.
-
17-12-2010, 09:59 PM #12
Re: Heat Pump Low Pressure Faults
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
-
17-12-2010, 10:40 PM #13
Re: Heat Pump Low Pressure Faults
only known 407c systems struggle in cooling in low ambient.heating should b good or have i had too many knight riders.tis d wkend!!!!
-
18-12-2010, 04:55 AM #14
Re: Heat Pump Low Pressure Faults
Heat-pumps tend to run a low suction pressure for some time directly after a cold start-up. Once the system gets itself moving towards equilibrium, the suction pressure will lift. Some manufacturers install a start-up timer which bypasses the LP trip until the system has stabilised.
It could be that the LP trip, or system setting, is actually a tad too high for prevailing conditions. Alternatively, there may be a start-up time delay function that can be modified.Last edited by desA; 18-12-2010 at 04:58 AM.
Engineering Specialist - Cuprobraze, Nocolok, CD Technology
Rarefied Technologies ( SE Asia )
-
18-12-2010, 01:18 PM #15
Re: Heat Pump Low Pressure Faults
A good point I am working on too. I have been drafting an article on the matter of HP operating characteristics in colder seasons to publish in the industry magazine currently publishing my thoughts. Like most articles I write - I write them because it is something I want to undertsand better - not because I already understand
Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.
Similar Threads
-
vacuum reduces when vac pump is isolated
By bill1983 in forum FundamentalsReplies: 40Last Post: 04-08-2009, 08:00 AM -
Sizing of Heat pump
By pinkpanther in forum Tools and CalculatorsReplies: 5Last Post: 24-05-2009, 08:16 PM -
Homemade Heat Pump...
By AC_Hacker in forum New to REReplies: 0Last Post: 29-04-2009, 11:30 PM -
Pool heat pump water side diagram
By nike123 in forum Heat PumpsReplies: 23Last Post: 22-03-2009, 07:42 PM -
frostles heat pump
By Lc_shi in forum New TechnologiesReplies: 27Last Post: 31-03-2008, 07:53 AM