    Heat Pump Low Pressure Faults



    During the past couple of weeks in the midst of the cold spell, we have attended several call outs to E4 (low pressure) faults on Daikin splits. Systems on R407C and in heating mode with the coils heavily frosting and not clearing fully on defrost.

    Even the one recently fitted in our office was showing E4. I thought that the apprentice had not pressure tested correctly so I got him to recover and re-test, only to find that it was sound with a correct charge!!

    Any one else been having these problems?



  2. #2
    Join Date
    Nov 2006
    Location
    UK
    Age
    50
    Posts
    708
    Rep Power
    23

    Re: Heat Pump Low Pressure Faults

    Not me personally but I do know a lot of engineers I associate with have had similar troubles during this recent cold spell

  3. #3
    Join Date
    Mar 2006
    Location
    Lancashire
    Posts
    1,859
    Rep Power
    28

    Re: Heat Pump Low Pressure Faults

    Yes we have also had a couple with the most recent being on a Lennox packaged unit that trips as soon as the temperature drops.

    I've got a post on here entitled "would a HGB work"
    The difference between genius and stupidity is that genius has its limits.

    Marc

  4. #4
    Join Date
    Sep 2007
    Location
    Split Croatia
    Age
    57
    Posts
    6,151
    Blog Entries
    6
    Rep Power
    36

    Re: Heat Pump Low Pressure Faults

    I think that is possible that during low temperatures R407C somehow fractionate partially (as oppose to R410A) and therefore low pressure alarm. I have that error frequently on air-to-water heat pumps of larger capacity with R407C and they are usually limited to -5°C outdoor air temperature working limit. I personally set them to use electrical backup heater when temperature is -2°C (which is rare in my location).
    Last edited by nike123; 12-12-2010 at 06:29 PM.

  5. #5
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Heat Pump Low Pressure Faults

    Quote Originally Posted by nike123 View Post
    I think that is possible that during low temperatures R407C somehow fractionate partially (as oppose to R410A) and therefore low pressure alarm. I have that error frequently on air-to-water heat pumps of larger capacity with R407C and they are usually limited to -5°C outdoor air temperature working limit. I personally set them to use electrical backup heater when temperature is -2°C (which is rare in my location).
    Internal fractionation causes higher pressures.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  6. #6
    Join Date
    Dec 2005
    Location
    Cheshire
    Age
    39
    Posts
    264
    Rep Power
    21

    Re: Heat Pump Low Pressure Faults

    Quote Originally Posted by frank View Post
    During the past couple of weeks in the midst of the cold spell, we have attended several call outs to E4 (low pressure) faults on Daikin splits. Systems on R407C and in heating mode with the coils heavily frosting and not clearing fully on defrost.

    Even the one recently fitted in our office was showing E4. I thought that the apprentice had not pressure tested correctly so I got him to recover and re-test, only to find that it was sound with a correct charge!!

    Any one else been having these problems?
    Not in work but when I've been at my gym one of the Daikin spits goes onto E4 on both cooling and heating. Think its R407c but didnt look into that far.

  7. #7
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Heat Pump Low Pressure Faults

    Forgot to mention.....

    We have also had this happen on a 3 pipe RSEYP8.

  8. #8
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Heat Pump Low Pressure Faults

    Quote Originally Posted by Slim R410a View Post
    Not in work but when I've been at my gym one of the Daikin spits goes onto E4 on both cooling and heating. Think its R407c but didnt look into that far.
    If it's an E4 fault on both heating and cooling then it may have lost it's gas and be a genuine LP fault.

  9. #9
    Join Date
    Dec 2009
    Location
    England
    Age
    41
    Posts
    29
    Rep Power
    0

    Re: Heat Pump Low Pressure Faults

    I have had a e4 fault code before on a sililar system but the charge was fine, The problem was a defective p.c.b on outdoor unit. I changed the p.c.b and got it back up and running again.

  10. #10
    Join Date
    Apr 2010
    Location
    england
    Age
    50
    Posts
    12
    Rep Power
    0

    Re: Heat Pump Low Pressure Faults

    could be lp sensor/transducer.get ur gauges on,run it and watch the gauge.if the comp starts to drive the back pressure to where u wanna be then goes into fault its ur faulty lp.check with "technical help desk!"on resistance readings before u change the pcb

  11. #11
    Join Date
    Oct 2001
    Location
    Nottingham UK
    Posts
    5,668
    Rep Power
    51

    Re: Heat Pump Low Pressure Faults

    Looking at some of the replies to this thread, it's obvious that the main point has been missed.

    The cold weather has caused the R407C to reduce in pressure below the set point of the LP switch/sensor.

    Once the ambient has increased the LP fault goes away, without any loss of charge.

    Please re-read the original post.

  12. #12
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Heat Pump Low Pressure Faults

    Quote Originally Posted by jimmy wilkes View Post
    could be lp sensor/transducer.get ur gauges on,run it and watch the gauge.if the comp starts to drive the back pressure to where u wanna be then goes into fault its ur faulty lp.check with "technical help desk!"on resistance readings before u change the pcb
    Voltage readings on transducers - resistance readings on thermistors.
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

  13. #13
    Join Date
    Apr 2010
    Location
    england
    Age
    50
    Posts
    12
    Rep Power
    0

    Re: Heat Pump Low Pressure Faults

    only known 407c systems struggle in cooling in low ambient.heating should b good or have i had too many knight riders.tis d wkend!!!!

  14. #14
    Join Date
    Mar 2009
    Location
    KZN, South Africa
    Age
    64
    Posts
    2,212
    Rep Power
    20

    Re: Heat Pump Low Pressure Faults

    Quote Originally Posted by frank View Post
    Looking at some of the replies to this thread, it's obvious that the main point has been missed.

    The cold weather has caused the R407C to reduce in pressure below the set point of the LP switch/sensor.

    Once the ambient has increased the LP fault goes away, without any loss of charge.

    Please re-read the original post.
    Heat-pumps tend to run a low suction pressure for some time directly after a cold start-up. Once the system gets itself moving towards equilibrium, the suction pressure will lift. Some manufacturers install a start-up timer which bypasses the LP trip until the system has stabilised.

    It could be that the LP trip, or system setting, is actually a tad too high for prevailing conditions. Alternatively, there may be a start-up time delay function that can be modified.
    Last edited by desA; 18-12-2010 at 04:58 AM.
    Engineering Specialist - Cuprobraze, Nocolok, CD Technology
    Rarefied Technologies ( SE Asia )

  15. #15
    Join Date
    Nov 2010
    Location
    London
    Posts
    624
    Rep Power
    15

    Re: Heat Pump Low Pressure Faults

    Quote Originally Posted by desA View Post
    Heat-pumps tend to run a low suction pressure for some time directly after a cold start-up. Once the system gets itself moving towards equilibrium, the suction pressure will lift. Some manufacturers install a start-up timer which bypasses the LP trip until the system has stabilised.

    It could be that the LP trip, or system setting, is actually a tad too high for prevailing conditions. Alternatively, there may be a start-up time delay function that can be modified.
    A good point I am working on too. I have been drafting an article on the matter of HP operating characteristics in colder seasons to publish in the industry magazine currently publishing my thoughts. Like most articles I write - I write them because it is something I want to undertsand better - not because I already understand
    Only the dogmatist says he will never change his mind. We all know that some of our opinions are wrong but none of us know which they are for if we did then they just wouldn't be our opinions. - JS Mill.

Similar Threads

  1. vacuum reduces when vac pump is isolated
    By bill1983 in forum Fundamentals
    Replies: 40
    Last Post: 04-08-2009, 08:00 AM
  2. Sizing of Heat pump
    By pinkpanther in forum Tools and Calculators
    Replies: 5
    Last Post: 24-05-2009, 08:16 PM
  3. Homemade Heat Pump...
    By AC_Hacker in forum New to RE
    Replies: 0
    Last Post: 29-04-2009, 11:30 PM
  4. Pool heat pump water side diagram
    By nike123 in forum Heat Pumps
    Replies: 23
    Last Post: 22-03-2009, 07:42 PM
  5. frostles heat pump
    By Lc_shi in forum New Technologies
    Replies: 27
    Last Post: 31-03-2008, 07:53 AM

Posting Permissions

  • You may not post new threads
  • You may not post replies
  • You may not post attachments
  • You may not edit your posts
  •