09-12-2010, 11:09 PM #1
Header sizing
Hi All,
after long search on the net, i couldn't find anything for sizing the refrigerant header. Any recommendations or formulas, or at least, where to take a look, some links or other sources would be appreciated....
-
10-12-2010, 04:41 PM #2
Re: Header sizing
It depends what header you mean: suction or discharge
Acording to the bitzer recomendations:
The diameter of suction header should be selected so that gas velocity at full load doesn't exceed 4 m/s
The cross section should at least correspond to the total of the cross section of the individual discharge line sectionIn some places will have to think ...
-
11-12-2010, 07:35 AM #3
Re: Header sizing
Thanks, i will check this calculation today and than i come back...
-
12-12-2010, 09:13 AM #4
Re: Header sizing
HEADER CAN BE ALSO BE SIZED VIA SLKEN PROGRAM . USE THE TOTAL REFRIGERATION LOAD TO FIND OUT THE HEADER SIZE .AND INDIVIDUAL DISCHARGE/ SUCTION LINE CAN BE FOUND WITH LOADING PROGRAM WITH INDIVIDUAL REFRIGERATION LOAD.
SEND ME A PM ddk0123@gmail.com and i will send you the SOLKEN SOFTWARE . GIVE THE TECH DATA SOTHAT I CAN DO THE SELECTION OF HEADERS .
-
12-12-2010, 04:19 PM #5
Re: Header sizing
Did you meant the SOLKANE software?
If yes which module?
Similar Threads
-
A/C Chiller Sizing tables
By romaurie in forum Tools and CalculatorsReplies: 1Last Post: 12-12-2010, 01:04 PM -
Water velocity in water header
By wilsoncheung in forum FundamentalsReplies: 3Last Post: 12-12-2010, 12:56 PM -
Capillary tube sizing
By Sledge in forum RefrigerantsReplies: 7Last Post: 16-11-2010, 11:44 PM -
Copper Pipe Sizing Tool.
By Testech in forum Tools and CalculatorsReplies: 14Last Post: 21-01-2010, 01:13 PM -
Sizing for Australia
By dogma in forum FundamentalsReplies: 5Last Post: 17-03-2006, 10:05 AM